Discuss Volt free vokera gas boiler in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Just wondering can anybody help me. The boiler I'm working with is a vokera verve combi boiler.
the house has a three zone programmer so hot water, first floor rads and second floor rads each controlled by a 2 port motorised valve..

the basement of the house has underfloor heating..

there is a external pump for the rad circuits but the problem I'm having is for example if I call for first floor heating how do I get the pump to turn on at the same time.. Correct me if I'm wrong but I don't have 230 volts at my boiler so in turn cannot switch my pump on..

how do I turn on the pump with a voltage free contact boiler..


Currently at at the moment my circulating pump is constantly running from another power source,, this is temporary so the pump will circulate the heat for me..
 
Have the valves operate an 8 pin relay, this gives you two 'volt free' switches from the valves, use one to operate the boiler and one for the pump.

I assume the boiler has a LV switchlive or similar from your description, otherwise just come to it to the switch live if it's 240V
 
Just wondering can anybody help me. The boiler I'm working with is a vokera verve combi boiler.
the house has a three zone programmer so hot water, first floor rads and second floor rads each controlled by a 2 port motorised valve..

the basement of the house has underfloor heating..

there is a external pump for the rad circuits but the problem I'm having is for example if I call for first floor heating how do I get the pump to turn on at the same time.. Correct me if I'm wrong but I don't have 230 volts at my boiler so in turn cannot switch my pump on..

how do I turn on the pump with a voltage free contact boiler..


Currently at at the moment my circulating pump is constantly running from another power source,, this is temporary so the pump will circulate the heat for me..

cheers for the advice
 

Reply to Volt free vokera gas boiler in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Just under 2 years ago my central HVAC died. I wanted to go with a heat pump because the only appliance in the whole house that used natural gas...
Replies
0
Views
895
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
As a young man, I was an electrician, but now I'm getting on, I am strictly DIY. I used to have a cheap old 900W petrol generator connected to a...
Replies
8
Views
1K
Hi people, I’m new to the forum, first post so here goes. I’m wiring a heating control system and at the moment the customer wants as follows; A...
Replies
0
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock