3 X 60 watt fittings = 180watts me thinks, getting the initial values right may help you.Think you just type error as you summed it as 180w.so for say 3 60w fittings. 120w/230 =0.8a 66% of this is 0.53?
1x 13a socket say its total load is 12a so theres no diversity for this. so could i then say 12.53 is my design current (Ib)
So vd = (9.5 x 12.53 x60) / 1000
So vd is 7.14.
Now do i use 6.9 for lights or 11.5 for power to see if the Vd is acceptable. Sorry for the questions just wana get it straight. Thanks