Discuss Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

pencilpusher

Hi all

If an outdoor circuit comprises 2.5mm SWA running to adaptable box where it then splits into 2 x 1.5mm SWA cables for lighting, socket etc. how is the VD calculated?

I presume the VD for the 2.5mm run is calculated up to the adpatable box and added to the 1.5mm VD for each additional cable run present?

I would normally calculate on the smallest cable size present as a worst case scenario but was wondering what the alternative way is for the cables present.

Thanks

PP
 
Last edited by a moderator:
Supposing though that at the end of each leg of the smaller cable you had the same load, then wouldn't it be conductors in parallel? For arguments sake, if it was a 100W lamp, then wouldn't you be doing the calcs based on 200w down 3mm?? (also assumes both legs the same length).
 
Mostly voltage are drop at your homes because of the more than load of energy when you use the energy overloaded then you face the drops of voltage

Please may we have that again, only in English this time?
 
Mostly voltage are drop at your homes because of the more than load of energy when you use the energy overloaded then you face the drops of voltage

I know what voltage drop is and why it occurs. I don't, however, understand a word of this!
 
Last edited by a moderator:
Supposing though that at the end of each leg of the smaller cable you had the same load, then wouldn't it be conductors in parallel? For arguments sake, if it was a 100W lamp, then wouldn't you be doing the calcs based on 200w down 3mm?? (also assumes both legs the same length).

Hmmm, this has got me thinking now! Views?

PP
 
Last edited by a moderator:
It gives the same VD...

haven't done the maths so happy to be corrected, but if you go by the BGB tables then they are non-linear, so not sure about that.
 
Yes, in my tables the resistivity differs between 18.1-18.3 mΩmm²/m depending on the csa. But there is no meaning in trying to calculate the VD with a mV precision.
 
Yes, in my tables the resistivity differs between 18.1-18.3 mΩmm²/m depending on the csa. But there is no meaning in trying to calculate the VD with a mV precision.

Thanks but that is not the point though. My OP was about the correct way of doing it, not weather it was worth bothering with precision. I will stick with adding the VD up as previously mentioned.
 
Last edited by a moderator:
^^^ agree entirely. But it's been a slow day here at Rockingham Towers, so......
 
I thought voltage drop was what happens when the CU is upstairs, and all the sockets and lights are downstairs, so the volts all drop down the wires to the electrical stuff. Anyone know where my electric stopcock is?

Cheers.........Howard
 
Anyone know where my electric stopcock is?

should be in the attic. water flows downhill as well as volts.
 

Reply to Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
379
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
865
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock