Is there a voltage drop from DNO transformer to incoming supply? For a standard 100A supply to a house so they design cable to with stand no VD as so at maximum demand there will be no VD. It is then up to us to design circuits as to have as little as possible so that 230v remains everywhere. Of we design badly would the company's VD calcs be wrong as less voltage more current. And I'm I right in thinking overload on a cable would result in a higher VD to that circuit as they must be linked.
 
The point where the supply enters the house system is beyond your control but you will find that it is usually well above 230V. More likely is 235-250V so you have a considerable amount of spare capacity. As the current flowing in the cable increases the temperature of the cable increases and this causes voltage drop to increase. In other words VD is a product of the action of current flowing not a cause.
 
There is a voltage drop from transformer to incoming supply, because there is resistance in the cable, however the supply company work to ensure that the voltage supplied to houses / industry remains approximately constant.

You would tend to find that for a row of houses where the start of the row is close to the transformer and then (assuming they were all using the same supply) the voltage at the first house would be higher than that at the end of the row.

In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.

Where a new housing estate is built that will increase the demand on the supply and cause a drop in voltage.
The DNO therefore then needs to assess it's supply characteristics and ensure that the additional demand does not drop local voltage below the above limits.
On a temporary basis there may be high demand industry that may cause local fluctuations in the voltage.

BS7671 uses the "nominated" voltage of 230V as a standard reference voltage so that all calculations will be consistent. UK equipment is designed to be able to work (in the main) safely with the possible range of voltage available.
 

Reply to Voltage drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
729
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
620
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
910

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock