I have built an air flow bench using vacuum cleaner motors and there is a voltage fluctuation from the wall of around +-4 volts.

This is causing the readings on the manometer to be erratic and is defeating the object of the project.

Is it possible to stabilize the voltage to accurace of 99.5%?

Thank you.
 
I don't think you will get an AC-output stabiliser stable to 0.5% off-the-shelf or at a sensble price. No commercial equipment requires this stability - note the distinction between stability (voltage not changing) and accuracy (knowing what the voltage is). I would also be surprised if vacuum cleaner motors are that stable, for example the IR drop will vary with winding resistance which varies with temperature.

I would suggest using a closed-loop control system, where the controlled variable is monitored and used to correct the motor voltage. If you want constant speed, then you could use an optical tacho looking at a black sector painted on the fan impeller visible through the suction eye. If you want constant pressure (removing the fan curve from the delivery characteristic) then get the feedback from a pressure sensor. This kind of system will give you your 0.5% but setting up a PID controller is a bit complicated to describe on a forum!

BTW what engines do you tune?
 
Can you find any ordinary voltage stabiliser that will work to 0.5%?

One way I might tackle it it is to run the motors on DC (normal vacuum motors are universal and actually run slightly cooler and quieter on DC). An old machine spindle drive would do nicely, if a single-phase unit could be found or a 3-phase one hacked to run on single. The tach input would have to be referenced to the output.

Alternatively, a functional but Heath robinson solution would be to transform the incoming AC down, rectify and then add an isolated, stabilised DC supply in series, of say double the voltage fluctuation it needs to correct. Then, by taking its feedback not from its own output but by a suitable fraction of the motor voltage, it would adjust its output to stabilise that. With careful adjustment of the loop gain and compensation to keep it stable, I don't think there would be any trouble achieving the 0.5%.

A nice form of AC voltage stabiliser that can achieve good accuracy although with a slow response is the old servocontrolled Variac. By working it through a buck/boost step-down transformer you can trade accuracy with controllable range, by changing taps on the bucking transformer. Again no difficulty in reaching 0.5% but first you have to find / make your motorised Variac.
 
I don't think you will get an AC-output stabiliser stable to 0.5% off-the-shelf or at a sensble price. No commercial equipment requires this stability - note the distinction between stability (voltage not changing) and accuracy (knowing what the voltage is). I would also be surprised if vacuum cleaner motors are that stable, for example the IR drop will vary with winding resistance which varies with temperature.

I would suggest using a closed-loop control system, where the controlled variable is monitored and used to correct the motor voltage. If you want constant speed, then you could use an optical tacho looking at a black sector painted on the fan impeller visible through the suction eye. If you want constant pressure (removing the fan curve from the delivery characteristic) then get the feedback from a pressure sensor. This kind of system will give you your 0.5% but setting up a PID controller is a bit complicated to describe on a forum!

BTW what engines do you tune?


1)Someone else mentioned close loop system. I don't quite understand that. Is this a system where there is some feedback device (mechanical or electrical) that can keep the characteristics constant?



2) Just small block 1.4 16v Head
 
A vacuum cleaner motor might not be the best choice especially if it's a series configured motor with brushes which will be prone to speed changes with varying static pressures across it.
 
There are three motors in the bench. Each one using it's own power supply on separate sockets to prevent over load.

If there a way to have a display unit that can read all three voltages and display the average?

If there is then the problem is solved because I can then take all my manometer readings when the voltage hits 235V.

The UPS machine 2kva was very expensive.
 

Reply to Voltage Flucuating /Stablizer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
I am curious about voltage ratings on wire. I'm interested in 10-4 for a 25-foot cord that will be carrying 25 Amps at 240 volts. There are two...
Replies
13
Views
1K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
615
Hi, We are working on a Solar installation in the UK and have been asked to replace the string cable terminations, 6mm² yellow insulated ring...
Replies
4
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock