Hi guys,

Currently have some 221 wago connectors and looking at the 222 connectors around the same price. Am I right in saying that the 222 connectors would be classed as maintenance free in a wago box but not the 221's?

Thanks
 
As far as I'm aware...

222's are maintenance free (along with the 773 push fits) when used in a standard Wagobox or a Wagobox XLA.

221's are maintenance free (along with the 2273 push fits) when used in a Wagobox XL.

If you use the plastic sleeves to say mount the compact connectors in a Wagobox or a Wagobox XLA, they cannot be used in maintenance free configuration.
 

Reply to Wago advice needed about type and maintenance free connections in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
687
Hi all, I am about to fit a light fitting and wanted some advice whether I should just connect the light cables into the correct terminal blocks...
Replies
2
Views
619
Hi all, I’m after some advice regarding use of Wago boxes for adding a spur off a ring final. Is it okay to use a MF Wagobox with 221 Wago...
Replies
10
Views
3K
Hi all, DIY'er here looking for a bit of advice so please go easy on me. In my dining room there is an existing single pendant and i would like...
Replies
6
Views
464
I have come to extend a ring main on the old wiring (red and black) and have used the wago 222 connectors to extend each leg and extended each leg...
Replies
15
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock