chrisgc

Hi all,

My brother has not long called me and has informed me that the washing machine keeps tripping the RCD.

Just wondered the inspection procedure to narrow down the actuall fault?

Any info would be much appreciated.

Chris
 
Turn off machine and reset RCD. Then see which part of the machines cycle trips the RCD good chance it will be when the machine starts to empty and the pump kicks in.
 
Turn off machine and reset RCD. Then see which part of the machines cycle trips the RCD good chance it will be when the machine starts to empty and the pump kicks in.

Would my PAT tester determine any faults on the machine OR is it more likely to be a fault on the circuit it is plugged into??

Chris
 
I would say most likely the fault would be on the machine but i have been known to be wrong.
 
guess at machine as well.often be the heater element, esp. if you are in a hard water area. to poove or disprove, i would first do a PAT on it, then if no fault apparent, try it on a cold wash.
 
It might pick up the fault if the machine is at the part of the cycle that is casusing the problems. Easiest thing to do is disconnect the machine and then test the RCD to ensure it is functioning correctly. Then you will know circuit or machine.
 
Washing machines are a pain! Your PAT may show a fault but I think unlikely, as said before, more likely on a specific cycle the machine is on
 
It might pick up the fault if the machine is at the part of the cycle that is casusing the problems. Easiest thing to do is disconnect the machine and then test the RCD to ensure it is functioning correctly. Then you will know circuit or machine.

Not totally sure what stage of cycle it is at.

But it has only occured today and has tripped a few times ALSO have been told by my brother that there is still water in the machine (guessing they decided not to continue trying the machine as kept tripping).

So do you think maybe the following:

1 - Pat Test machine (after checking plug etc)
2 - If above all fine then checking socket outlet.

What other possible tests might I need to try?

(Just dont want to be wasting time if its a machine problem).
 
If you don't want to waste time if it is a machine fault then just test circuit and RCD job done.
 
90% of the time if its not the kettle or toaster, its the washing machine.
 
Yep prove the circuit is healthy.
 
If the circuit and rcd is given the all clear
Test the heating elements, and then a very possible culprit "the motor"
Right sods for earth faults

It has been known for some people to dis connect the earth strap to the motor, just to see if the tripping dis appears I believe.
Naughty hey
 
bugger the element. do cold washes and save on the leccy bill
 
had this fault on our own machien is under warrenty still so just got them out to it how ever it turned out to be a circuit board that has gone twice in the last 12 months
 
what make is the machine, so i know not to buy one like yours
 

Reply to Washing Machine Tripping RCD?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hj our washing machine tripped out electrics the other day. Everytime we switched it in the electrics cut out. We noticed a larger bend in the...
Replies
0
Views
444
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
581
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
821
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock