Discuss Weatherproofing SWA armoured cable through wall in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
I have a slightly odd requirement that means I am wanting to route a 3 core 4mm SWA cable (14mm outside diameter) from outside through a cavity wall into a garage to the isolator just inside. The cable is actually carrying DC feed from a small solar ground installation.

How should I shield the cable at the point it enters the wall so no water can get in?

I was thinking of a small IP55/65 junction box with a hole through the rear and a gland on the bottom but it means threading the box onto the cable before feeding into the wall which is a bit awkward. I know I could terminate it into the enclosure and then run dc cable through the wall but it is a seafront location and it seems far more sensible just to do the termination the other side of the wall straight into the isolator.

Are there any other options such as a large wall plate like I would use for coax?
 
To really seal it then an IP68 style gland on to a plate sealed against the wall.

But usually you just drill the hole through sloping slightly down towards the outside so any water will run out the way.

Also remember that the minimum bend radius of cables like SWA is usually about 8 times the diameter, so you are looking at 112mm radius or around 22cm diameter pipe as you guide for bending.

If that canot be met on your route then terminating in an IP68 box outside and running the cables in via some conduit or similar for physical protection is another option.
 
Thanks for the quick response.
I did at first think of a plate and gland but dismissed it as a bit DIY. I partly planned to use a box to preserve the bend radius within the box but there aren't many ideally shaped boxes it turns out. Luckily it is right under a soil pipe so any protrusion of the cable is negligible. I will definitely drill on a slope.
I don't want to use a metal plate due to location so guess it will have to be a bit of upvc unless you have any better suggestions? If it all looks awful I may revert to termination and conduit.
 
If you terminate the SWA to a box properly (i.e. metal SWA gland and attach earth wire to it via the "banjo" or Earthing Nut or similar) then you might be OK to take just the cores inside if they are physically protected by conduit, either earthed metal or PVC, all the way in to the isolator indoors. Then your bend radius per core is probably a couple of cm and easy to meet.

That way the outdoor box can be fairly small as it need not accommodate the SWA's bend radius.
 
Last edited by a moderator:

Reply to Weatherproofing SWA armoured cable through wall in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am planning to install wall lights such as these ones (LAP Bronx Outdoor Up & Down Wall Light Black - Screwfix -...
Replies
5
Views
698
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, I am burying a fiber optic cable so I have internet in my garage. I have purchased the following flexible conduit to run the fiber optic...
Replies
2
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock