So I am doing an insulation resistance test on a new flat and I get a dodgy L-E reading on the IR. I won't go above 20Meg and it fluctuates. Identified where the problem is and its a switched spur. When cables are removed all test +299 including the load which is 2 sockets. When all are put back in spur, the load gives the same dodgy reading. Replaced the spur and still get the reading. Any thoughts?
 
Could well be the spur, damp possibly. Only one way to find out, replace it or Wago all conductors together at the spur point and retest.
 
So replacing it has resolved it?
Have you IR tested the spur itself with nothing connected.
 
Load side L leaking to real earth but not to its own CPC, which is well insulated from earth. So you only see it when supply and load CPCs are connected together. Try testing between load L and supply CPC with the FCU removed.
 
Re#7: I may be a but thick today (in pain with my new knee after its total replacement) but should your explanation read:

'you only see it when supply and load Ls are connected together.'

Then your final sentence makes sense.
 
I prefer my version. Suppose the load L is damaged somewhere along the cable and leaking to the building structure or ground, but the CPC is not in contact with ground as the fittings are in dry studwork. Measuring L-E in the load cable alone will not reveal the fault due to the floating CPC. But the supply CPC, in contact with the building and ground through the bonding / main earthing, will be connected to the fault. Thus when the FCU is installed, even with the switch off the load cable will now read faulty as the CPCs are connected together.

BTW good luck with the knee. Do the exercises! Gave my mum her mobility back, has been marvellous, after ten years she can't tell it's not her own.
 
I think a take-away from this interesting problem is the importance of not only doing pair-wise IR readings for the supply cable and then the load cable but also to do the cross-pairs between conductors of the supply and load cables .
 

Reply to Weird IR results? At a Switched Fcu in RFC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
618
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
485
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
651
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
875
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock