Discuss Welder "must be connected to a 30A fused spur" in the Australia area at ElectriciansForums.net

G

Guest112

My old man just rang me wants to buy a welder but the manufacturers instructions say the welder has to be connected to a 30A fused spur, He hasnt bought it yet he said hes going to get more details for me tomorrow which ill post up,

From what i gather this'll have to be on a dedicated circuit but ive never heard of a 30A fused spur and can't find them online.

Anyone heard of these or know where to get them or installed one of theses welders before?

Any information would be great, I'll post the extra info as soon as i get it on here.

Thanks
 
bear in mind that a "30A fused spur" can be renamed a 30A fused radial. i.e. referring to the circuit, not a FCU. then it makes sense. a 30A radial circuit ( 4mm) protected by a 30Afuse ( or 32A MCB. )
 
bear in mind that a "30A fused spur" can be renamed a 30A fused radial. i.e. referring to the circuit, not a
FCU. then it makes sense. a 30A radial circuit ( 4mm) protected by a 30Afuse ( or 32A MCB. )

my thoughts also mate i was considering connecting the welder to a commando socket and just protecting the circuit from the db
 
sounds like a plan. esp if you've got some 4mm or 6mm T/E left over from a job.
 
My old man has one of those welders.
Was thinking of going 6mm2 T+E (have a length going spare) from a 32Amp MCB covered by an RCD into a 32A Commando socket and putting commando plug on the welder.
However when I opened the welder box to have a look at the data plate, the cord supplying the welder is 1.5mm2 H07RNF LNE, which unless my head is up my rear end (wouldn't be the first time either) is only rated to 16 amps.
Data plate on the welder has a max I1 value of 36.8A and a nominal value of 11.8A, welder itself is internally fused at 22A.....So now considering a 16A Type C / Type D MCB (still covered by RCD) and 16A Commando socket and plug. Only concern is start up current draw might cause nuisance tripping even with the Type C or D MCB.....as welding is a hobby for my old man so can take him a bit to get a weld struck properly.
Thoughts?
 
bear in mind that your Zs will have to be considerably lower on a type c or d MCB. 6mm should take care of that if you have a nice low value of Ze.
 
The CU in the Garage is a dual RCD board, which would need some minor mods to fit a non RCD protected circuit.....might be an option though. However knowing my dad...it likely will get used outside so will need to be RCD protected...and he is one of "those" who are deliberately ignorant of electricity....so RCD protection might be a good thing.
I need to check the Ze...thanks. The house ratings are fine and the Garage is fed off a short run of 6mm2 mechanically protected T+E so hopefully Ze should be ok. (Though just remembered that the guy who replaced the house CU stuck the garage on the house RCD....so need to sort that to regain discrimination........my old man and "time served boys" recommended through the pub or other dubious means, none of them who have any clue seemingly.
 
Last edited:
The 32A rating is for when the arc is first struck and the transformer / choke saturates. Once saturated the current drops. If you do lots of little tacks expect trouble.
Glad I’ve only had to work on industrial sets. Mind you a moron welder can cause plenty of damage. “There’s something wrong with the 63A plug and cable, it’s smoking!” I’ve near strangled them with the earth clamp lead.
 
dunno about welders, but i could name a few plumbers i would like to connect to a 30A socket.
 
hmm decisions decisions.....manufacturers guidance fair enough but how can you justify the lack of overcurrent protection for the flex supplying the welder? (32 amp breaker covering flex rated at 16 amps)
 
Chinese made welder, warranty provider is an austrian firm....Walter Werkzeuge Online Shop | Werkzeuge direkt vom Hersteller | GĂĽnstiges Werkzeug fĂĽr Heimwerker, their own welders are higher price bracket (though they still sell the same crappy hand held face shield), also no mention of said aldi welder on their site, though they do deal with the powercraft brand. (likely not updated for months).
Could well be that the welder was designed for another market, I'm thinking chinese market as their approach to electrical safety is a bit different to ours (2.5 Kw kettle on 0.75 flex and 13A fuse in plug.....CE approved so trading standards not interested, especially as major uk brand name on box....flex gets rather hot to put it mildly...so back it went)
 
Last edited:
So the final decision was......go with manufacturers instructions, as the old man doesn't want it to trip if he is tacking or welding on the driveway (personally I was going to try it hard wired to a 16A circuit on full bore and see if it pops a type C 16A, but he as the client doesn't want the chance of it popping while he is using it and I'm elsewhere), so a 32A circuit covered by one of the sheds RCDs, connected to a 32A commando socket, 32A commando plug on the welder (which I need to do something to as the 1.5mm2 cord is too small for the cord grip....thinking non conductive sealant between the cord and the outside of the plug cord entry to stop the cord being pulled out and stop moisture ingress)
Next thing is finding a 32A commando extension lead, have a couple of options (ebay being one), screwfix sell the plugs but no 32A leads...
 

Reply to Welder "must be connected to a 30A fused spur" in the Australia area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I am a DIY person (ie. not a qualified electrician) so I am sure this is a basic question but please bear with me. I am looking to add a...
Replies
6
Views
3K
Hello. I am installing a CCTV system for my mum. It's a basic IP camera setup, with up to 4 cameras and a recorder. I plan to have the NVR in the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock