Over the holiday period my partner returned home to her apartment with no power. None of the internal breakers in the consumer unit had tripped and so she was unsure what to do. She called an electrician who took the cover off the consumer unit and then showed her these singed breakers across the board. The main fuse had blown (which sits outside the apartment in the lobby) and that was replaced by the electricity company and the electrician replaced the entire set of breakers and RCDs in the consumer unit, without providing any explanation for the fault. He said the consumer unit is approx 15 years old, which we understand to be correct.

The electrician charged approx 4x the appropriate cost for each breaker and RCD and aggressively overcharged for the time, and I feel my partner was taken for a ride here. When I found out about this event I asked another electrician to come and assess the new work and to help diagnose why we have a fault in the first place. The second electrician, upon seeing these photos, suggested that the first electrician had taken a lighter or flame to create these burn marks across the unit and created a situation of duress so he could do emergency work at holiday rates.

The quality of the replacement work is not great, two of the RCDs are too small (40 amp instead of 64) and he has forced and bent some of the connection terminals to make the breakers fit the buss bar. The second electrician is quoting a tiny amount of money (and an appropriate amount) compared to the first to upgrade the RCDs that are too small and tidy up the breakers that don't properly fit the buss bar. I know trades often insult the work of other trades, but the second electrician was much more candid and helpful and clearly pointed out additional risks, and even offered to liase with the first electrician to try and rectify the issues instead of charging us to repair recently done shoddy work.

So the question, is this what really happened?


29be4ec9-d6cc-4b01-a4fb-d81eeefe6fd9.jpg
 

Attachments

  • 1749061e-dcbc-4efa-8e04-57138d147798.jpg
    86.1 KB · Views: 82
There may well have been tampering on your board (although that wouldnt be my first thought), but what caused the main supply fuse outside to blow initially? Has there been a surge caused by something? Was anyone else's main fuse affected?
 
Random blobs of soot and scorching will not appear on the underside of MCBs and RCDs just like that. It does look like deliberate sabotage.

If terminations are left loose on equipment they can overheat due to excess resistance. The heat is generated in the metal parts and conducted along them, so it is almost always the plastic that is in direct contact with metal that gets scorched. An overheated loose terminal in an MCB or RCD, for example, will be burnt right around the entry hole in the casing, and as the heat conducts along the cable, its insulation will also be burnt. Plastic that is further away from the terminal will be less affected. Internal faults in devices can also lead to parts of the casing becoming overheated. In the case of MCBs and RCDs the most likely internal problem would be arcing or high resistance at the contacts, in which case the scope of damage will be defined by the shape of the metal parts.

High-energy surges like lightning strikes can cause flashovers and cause areas of scorched insulation that do not tie in to conductors being overheated. But again, they will follow specific patterns and produce characteristic shapes and not just be random sooty blobs. Clearing a very high energy fault can even destroy a circuit breaker and burst its case open with the energy dissipated in the arc, but once more the damage will be focused on the area directly adjacent to the internal contacts, mainly on the inside, while the areas with the burn marks in your pics would be least affected.

As per DPG, there is still a question of what actually happened to begin with...
 
Keep these photos and take the lone ranger to court.
Obvious lighter burn on plastic. As explained above, a faulty mcb or loose cable would heat from the inside the casing.

That’s fraud. And I can assure you and any other members of the public that these few crooked tradespeople give the honest hard workers a bad name.
 
Last edited:
Thanks for the replies guys, it is sad to see other people agree with the premise and make the same points my second electrician made (no issues on the insulation or terminals).

As to DPG's point, it is obviously still a concern to me that the main fuse tripped. No other main fuses tripped in the building as we understand. My partner said she had put the washing machine on before leaving the house and when the power returned the machine continued on from where it had cut off in the cycle, so perhaps there was a fault in the machine, but nothing has repeated with use of the machine (and inconjunction with outer utilities on the same RCD) that have tripped anything.


The second electrician wondered if the old main fuse was a lower amperage than appropriate, but now it has been upgraded to 60 amps.
 
Last edited:
You've more here than just fraud..... technically that's also arson and criminal damage. I assume this cowboy was found via an emergency call-out service and as such is registered with a Part P scheme (Napit/NICEIC/few others). I wouldn't hold back with letting both that provider and scheme have two barrels, report the electrician to trading standards and the attempted arson to the Police.

You'll almost certainly never know what caused the upstream fuse to blow, for all we know the first 'electrician' could have made that happen deliberately, so that's not the issue any more.
 
You've more here than just fraud..... technically that's also arson and criminal damage. I assume this cowboy was found via an emergency call-out service and as such is registered with a Part P scheme (Napit/NICEIC/few others). I wouldn't hold back with letting both that provider and scheme have two barrels, report the electrician to trading standards and the attempted arson to the Police.

You'll almost certainly never know what caused the upstream fuse to blow, for all we know the first 'electrician' could have made that happen deliberately, so that's not the issue any more.

Thank you Rockingit. I should have added the additional context that this is an apartment in France, so the general recommendations make sense but the specifics I need to work out for that country, and my general understanding is that there isn't such a formal process.
 
Buy a cheap make mcb and a lighter and hold the flame underneath - you will discover what has been done.

With regards to the loss of power ask your wife to remember in detail what what powered up at the time - this is important to know lest the defence conjures up a freak but plausible explanation for what you can see. Most likely overloading and the protective devices have operated without drama or thermal 'scarring'.

I can provide you with a chap's name and his business who does forensic investigations and is an experienced expert witness in court.
 
I believe the process appropriate here, then, is interrogation by Madame Guillotine. 🪓💀
 
this is an apartment in France

I had guessed as much from the type of board, wire colours etc. We have a couple of members with local knowledge who might be able to add something. @Mike Johnson, for example...
 
Thats a external burn . Not from within the plastic etc etc . No question about it .BUT ...Not a chance in hell of winning or worth fighting . Unless there is photographic evidence that these marks where not present before he started work etc etc . Make threats, ask for 100% of money back might work . Bluff him. Tell him you have contacted local BC and his scheme etc and they want to investigate etc . But A good lawyer might say "dont go full legal" . If he has messed about .Chances are he will want to get away from it ASAP and hand the money back . Ive seen many "tricks " like this used by a very FAMOUS london Plumbing/electrical and all other trades Company . I wont mention their name .But I have seen them come unstuck on the steps of Courts a few times :)
 
Go on put on face book and shame this spark, what fooking cheek. He could have make more damage, what a idiot.
Bloody horse theif riding in the distance
With the moine, did you get idiot spark from the local saloon. On line.
 
Has the apartment recently been changed from three phase to singleI, looks like it from the colours of the phase conductors?

Is the apartment fitted with one of the new French smart meters by EDF? if so it could trip out with an overload or DC fault and then re-set itself, the incoming protection device is in fact a load limiting RCD not to protect the owner occupier but to stop the user from using more power than their tariff payment.
 
Has the apartment recently been changed from three phase to singleI, looks like it from the colours of the phase conductors?

Is the apartment fitted with one of the new French smart meters by EDF? if so it could trip out with an overload or DC fault and then re-set itself, the incoming protection device is in fact a load limiting RCD not to protect the owner occupier but to stop the user from using more power than their tariff payment.

Thanks Mike. Yes I believe you are correct, and second electrician has noted that it is on a 6kvh plan which he was surprised about and thought was low.

Could it be the case then that the smart meter RCD tripped and simply needed resetting and that was that. Perhaps the EDF person didn’t even need to change the main fuse (however that definitely occurred as my partner let the person in and they swapped out the fuse). She said they were there for 1-2 minutes tops and just switched it out.
 
Never seen anything like that, no damage to cable or in area of breaker I'd be expecting to see marks and no pattern to them. Never thought I'd say this but it does indeed look like someone has held a lighter to them.
 
Thanks Mike. Yes I believe you are correct, and second electrician has noted that it is on a 6kvh plan which he was surprised about and thought was low.

Could it be the case then that the smart meter RCD tripped and simply needed resetting and that was that. Perhaps the EDF person didn’t even need to change the main fuse (however that definitely occurred as my partner let the person in and they swapped out the fuse). She said they were there for 1-2 minutes tops and just switched it out.
That is an very low tariff, I would be surprised if it does not go off at regular intervals, I assume no electric cooking or tumble dryer as these seem to be the main culprits in these EDF switch off incoming RCD.

It's unusual for the main fuse to go, perhaps it was changed because it was faulty and the incoming RCD did it's job and just needed re-setting. Is it possible to see a picture of the main supply/meter and associated works?

Couple of other points, is there a cover for that consumer unit? if so put it back on, but at the least take the metal handle (broom) out of area.

And I agree with everyone else that has commented, that the first electrician was on a job creation scheme, never seen burning like that in a consumer unit.
 
Last edited:
That is an very low tariff, I would be surprised if it does not go off at regular intervals, I assume no electric cooking or tumble dryer as these seem to be the main culprits in these EDF switch off incoming RCD.

It's actually a pretty full fledged apartment with washing machine, electric cooker, electric (convection hob), microwave and tumble drier. It's an interesting comment because we've spent a whole bunch of time here including covid lockdowns with extra load on the system from additional laptops, ipads etc.

I ran some experiments today and ran the oven + microwave and got a live draw of 4.5 kva, so it does sound plausible that adding some extra appliance usage and this could trip.

Could there be any leniency in when the Linky trips? It was Christmas Eve when it tripped, perhaps the load in the whole building was pushing up on a limit?

It's unusual for the main fuse to go, perhaps it was changed because it was faulty and the incoming RCD did it's job and just needed re-setting. Is it possible to see a picture of the main supply/meter and associated works?

I've done some digging today and posted what I can find. Main fuse outside the apartment door and then the basement setup, which I think has one Linky for the building (the big one) and then another for an apartment that is on the basement level. I couldn't really get much out of the picture for the main fuse since it's mounted super high and I didn't have a ladder to hand.

Couple of other points, is there a cover for that consumer unit? if so put it back on, but at the least take the metal handle (broom) out of area.
Oh yes it's covered now, although I don't want to post the first electricians work and have the forum rip it even further to shreds. Mr second electrician's work I will post once he's done.

And I agree with everyone else that has commented, that the first electrician was on a job creation scheme, never seen burning like that in a consumer unit.
 

Attachments

  • IMG_0783.jpg
    10.1 KB · Views: 32
  • IMG_0786.jpg
    12.1 KB · Views: 32
  • IMG_0785.jpg
    12.9 KB · Views: 30
  • IMG_0784.jpg
    12.9 KB · Views: 29
  • IMG_0787.jpg
    9.1 KB · Views: 33
Are you suggesting there is only one Linky meter for the whole building?

Pictures are too small to provide any additional information and does not show the original consumer unit and its incoming supply.
 
Thanks to everyone for the help. @Mike Johnson in particular. Any additional direction on what to take photos of would be very helpful.

I think I understood what you meant now at least - on top of that consumer unit there is another box with the Linky and the load limiting RCD, but you can't see any wiring, it's all hidden. I've attached a hair of a photo and another example from the web, I'm pretty sure the RCD is the same as the example one.

As to your question about the building, my point was that in the basement there is a much larger Linky unit, when I scrolled through it's user interface it seemed to have a lot more data and some partitioned with the same title and different sub titles (e.g blah 1, blah 2, blah 3), so I wondered if that was some sort of master unit for the building, but I could be wrong.

Also, good shout on the subscription, EDF remotely increased it from 6kVA to 12kVA
 

Attachments

  • example.jpeg
    83.1 KB · Views: 14
  • IMG_0791.jpg
    259.6 KB · Views: 15
  • IMG_0761 (1).jpg
    283.9 KB · Views: 15

Reply to Were these breakers tampered with? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hi all, New homeowner here... hoping it's okay to seek some advice on a quote. I've recently had some wiring done for a new kitchen in a small...
Replies
27
Views
3K
I have carried out home wiring for 60 years as a competent person, for the last 20 years, I employ a local electrician to check my work and sign...
Replies
10
Views
1K
The above picture was taken at the festival of Britain and it shows a BTH bulk oil breaker, for me this represents the development of the super...
Replies
16
Views
3K
Long story short: I had a electrical problem on a circuit that powers our backyard lights and outlets a few months ago that fried the circuit...
Replies
2
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock