Discuss Wet Under Floor Heating Modification in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Reaction score
1
Hi Guys.

I have a flat with a 9KW electric boiler, dedicated for the wet underfloor heating system. The tenants have reported that all the digital room stats were not working, as when they increased the temperature to get more heat, nothing was happening. Within 15 minutes in the property I discovered that all the room stat controls were disconnected at the central chalk block terminals, There is a 1.5mm2 T&E cable running to each digital room stat from the main terminals, then the stats run on batteries, I'm thinking the T&E cables are simply carrying control voltages, although not entirely sure. I then noticed all the motorised valves had been disconnected from the flow & return manifolds, Further more the pump has been wired so its constantly running, when the 45A main isolator is on. Someone has basically just completely simplified the system, in a rather cowboy fashion.
Now I've suggested 2 ways forward to the landlord...

1. Re-instate the motorised valves & replace faulty room stats (battery leak on x2 stats) & correct the wiring, so the pump only runs when the system is putting out heat.

2. re-configure the central wiring & fit a Sallus wireless thermostatic time clock system, so the whole flat is operated from the one wirelessly operated thermostatic time clock.

My concern is wit the 1st option, I require a plumber to re-instate the valves & I know the landlord will be doing a refurb on this property as soon as its vacant, so he is very unlikely to go for a fix that costs upwards of £600, which I'm sure will happen here.

I think number 2 is the way forward, what I want to know with this is, do I need to take a 3-core from the PCB in the electric boiler to pick up the thermostatic control circuit, or can I just use the wireless thermostatic timeclock in a simply on off fashion, via the main switched live for the boiler.

Any insights, or help massively appreciated..

Thanks

Derek
 
If the best and safest way to repair this mess, and it requires the input and helpof a Plumber, then so be it Derek.
 
Have normal motorised valves been used? These systems normally use thermal actuators fitted onto the manifold.

Fitting a single thermostat to control all zones is not a sensible option unless you have the means of properly balancing the zones on the hydraulic side.
 
Fitting a single thermostat to control all zones is not a sensible option unless you have the means of properly balancing the zones on the hydraulic side.

Which you might need a plumber for in any case.
These systems are designed around sing zonal room thermostats for optimum efficiency so best revert back to it ….. Option 1
 

Reply to Wet Under Floor Heating Modification in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Hi. I'm installing a wet underfloor heating system in my own house. What would you recommend as the best smart control system? I can hardwire...
Replies
3
Views
662
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
642
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
687
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock