Discuss What are your thoughts on this 3ph domestic. in the UK Electrical Forum area at ElectriciansForums.net

Guys be gentle he's still in training and has much to learn positive comments will be much better. I agree the head must be verified if it is a true three phase. Also in agreement a total load must be calculated.
I would use galvanized steel trunking and feed to either to 3 phase consumer unit or use a ryefield board to balance load and distribute if more than one consumer unit is required. But as advised by others we need a load idea to advise further.
 
Guys be gentle he's still in training and has much to learn positive comments will be much better. I agree the head must be verified if it is a true three phase. Also in agreement a total load must be calculated.
I would use galvanized steel trunking and feed to either to 3 phase consumer unit or use a ryefield board to balance load and distribute if more than one consumer unit is required. But as advised by others we need a load idea to advise further.

If he's still in training why isn't he asking his boss or mentor?
 
If he's still in training why isn't he asking his boss or mentor?
that is a good point but the fact he has signed up to forum is positive and he has to learn as in some point in life he will need to be independent, so I would encourage him to think alone but ask his boss or mentor before carrying out any work
 
that is a good point but the fact he has signed up to forum is positive and he has to learn as in some point in life he will need to be independent, so I would encourage him to think alone but ask his boss or mentor before carrying out any work

Thanks Sajeel. Don't worry, I can take it on the chin. Its quite amusing really, I have seen this on many threads on here, you ask a question and the more experienced people spend more time criticising and trying to put people down that actually answering the question. I would expect it puts a lot of people off asking a question because you have to trawl through all the negativity to actually get to the odd reply that gives a constructive answer. Its a shame really, it almost defeats the object of having a forum for discussion.

I am a project manager in fire systems and very experienced in my field. Also having been a control systems engineer for many years I am very experienced in process industries. I am now self teaching electrical books etc and will have the odd question but it appears this forum is not the place for asking. If someone asked be a question relating to BS5839 a fire installation or a control systems related question I would gladly answer, not criticise or run them down or aggressively point out all the information they had not provided in the question. Perhaps ask them to expand on the question and point them at the information which was required.

In response to above, it will be a general domestic load, not warranting any more than a 100A supply so 3 phases would not be required. Yes it is a mess hence the rewire. Someone above (I assume experienced) stated it has PVC sheathed cables why rewire, my car has tyres but they need replacing from time to time, how do you know the condition of the cables from looking at the photo. Some other comment was why rewire, because the customer has requested a rewire. Another comment was to carry out an EICR, why? It is being rewired, would you get your car serviced before scrapping it to buy a new one? See on reflection, some of the hasty comments provided above have not been given much thought and have been about as constructive as cementing bricks with margarine.
 
Thanks Sajeel. Don't worry, I can take it on the chin. Its quite amusing really, I have seen this on many threads on here, you ask a question and the more experienced people spend more time criticising and trying to put people down that actually answering the question. I would expect it puts a lot of people off asking a question because you have to trawl through all the negativity to actually get to the odd reply that gives a constructive answer. Its a shame really, it almost defeats the object of having a forum for discussion.

I am a project manager in fire systems and very experienced in my field. Also having been a control systems engineer for many years I am very experienced in process industries. I am now self teaching electrical books etc and will have the odd question but it appears this forum is not the place for asking. If someone asked be a question relating to BS5839 a fire installation or a control systems related question I would gladly answer, not criticise or run them down or aggressively point out all the information they had not provided in the question. Perhaps ask them to expand on the question and point them at the information which was required.

In response to above, it will be a general domestic load, not warranting any more than a 100A supply so 3 phases would not be required. Yes it is a mess hence the rewire. Someone above (I assume experienced) stated it has PVC sheathed cables why rewire, my car has tyres but they need replacing from time to time, how do you know the condition of the cables from looking at the photo. Some other comment was why rewire, because the customer has requested a rewire. Another comment was to carry out an EICR, why? It is being rewired, would you get your car serviced before scrapping it to buy a new one? See on reflection, some of the hasty comments provided above have not been given much thought and have been about as constructive as cementing bricks with margarine.

I'm sure you can appreciate that information regarding electrical installations should not be given out freely to just anyone, as an unsafe electrical installation has the potential to kill people. To that end it would be remiss, in a professional, moral, and possibly legal sense, of forum members to not ask questions pertinent to the original question to clarify whether the OP is of a competent nature.
Some problems can arise when the OP thinks they are not getting the answer they expected or refuse to provide any additional information that may help forum members in assisting the OP.


In relation to your confusion about an EICR, it was suggested because full testing and inspection is the only proper way to ascertain the condition of the installation and final circuits. If the customer has requested a rewire then fine, that's up to them. But to use your car analogy, getting an EICR before a rewire is like getting a full MOT and inspection done on a car before deciding whether to scrap it or not. If it only needs a few bits doing to it then it might be foolish and costly to buy a new one as a matter of course.
It was not a hasty and ill thought out comment, but your criticism of it just goes toward displaying your own ignorance.
 
Another comment was to carry out an EICR,

why? It is being rewired, would you get your car serviced before scrapping it to buy a new one?

From YOUR opening post

"I am currently in training but this is a family friend and I have discussed carrying out a rewire for them once I get my papers."

Discussed is very different to going to be done.

You can't always determine the state of an installation by looking at the fuse board(s) - and whilst I agree that the photo you posted may show a mess it may not actually need a rewire!

Just saying.
 
From YOUR opening post

"I am currently in training but this is a family friend and I have discussed carrying out a rewire for them once I get my papers."

Discussed is very different to going to be done.

You can't always determine the state of an installation by looking at the fuse board(s) - and whilst I agree that the photo you posted may show a mess it may not actually need a rewire!

Just saying.
Blimey, its like chatting on a forum of barristers. May I strike my question and re-phrase said statement as "I have discussed carrying out the rewire as requested by them"
 
Guys be gentle he's still in training and has much to learn positive comments will be much better. I agree the head must be verified if it is a true three phase. Also in agreement a total load must be calculated.
I would use galvanized steel trunking and feed to either to 3 phase consumer unit or use a ryefield board to balance load and distribute if more than one consumer unit is required. But as advised by others we need a load idea to advise further.

What needs verifying? The head is a three phase head. The incoming supply at the suppliers terminals (outgoing side of meter) is single phase.

What you you feed from a ryefield board?

And for that matter who would pay for the completely unnecessary change to a three phase meter and the possibly increased electricity bill?
 
Davesparks I don't know why your cage is rattled there is nothing wrong with my comment based on the fact a 3 phase solution is required but a load calc will show that as stated in my post.
 
Last edited by a moderator:
Davesparks I don't know why your cage is rattled there is nothing wrong with my comment based on the fact a 3 phase solution is required but a load calc will show that as stated in my post so I suggest before opening your mouth THINK

A single phase supply has been provided by the DNO at the point of connection to the consumers equipment.
It is a domestic installation so normal load is going to be around 20A.
It'll cost a fair whack to have a three phase supply made available which will be completely unnecessary.

And as for fitting a ryefield board? What would that achieve unless there are a lot if submains to be run?
 
Guys, lets not argue. I believe my question has been answered. It is a 3 phase head, this is confirmed by the DNO. It is a single phase supply as Dave says the supply is the side of the meter available to the consumer, so in my case I ignore the fact it is a 3ph head, the relevance is the single phase at the meter tails.

For future reference for me Dave, my question would have been relevant I guess if a 3 phase meter had been installed and all phases made available to the consumer? Then, would I need to consider load balancing. If for instance this was still only a domestic supply loading approx 100A would you be expected by the DNO to utilise all 3 phases and split the loads evenly amongst them?
 
That's ok, it's only been said a half dozen times already in this thread.

Now, more importantly, did they say you could connect to the earth terminal in that cutout?
Dave, this is the existing earthing arrangement:
DSC01192.jpg
 
For future reference for me Dave, my question would have been relevant I guess if a 3 phase meter had been installed and all phases made available to the consumer? Then, would I need to consider load balancing. If for instance this was still only a domestic supply loading approx 100A would you be expected by the DNO to utilise all 3 phases and split the loads evenly amongst them?

If you had a three phase supply, and actually needed it, then he's you should look at balancing the loads across the phases. But very few loads in domestic are constant so in effect it will be almost impossible to actually balance it.
Up until a few years ago the regulations required points on different phases to be kept seperate from each other or clearly labelled as 415V being present. This is why a lot of houses fed with 3 phases are wired with each phase feeding a different floor. So ground floor L1. First floor L2, second floor L3.
This doesn't balance the phases very well but does achieve reasonable separation of the points.

If look at the effect on the customers bill of getting the meter changed to single phase first off if They had a 3 phase supply that was unnecessary, it may reduce their bill to have the smaller supply.
If a domestic install really has a normal/average load of around 100A then it will likely be an enormous house and already be utilising a three phase supply
 
Very true unless extension, basements and lofts have been added with electric showers or electric hob and ovens then load can exceed 100a easily I had one property that was tripping due to overload when I explained he required three phase head he was like I don't wanna spend that kind of money. I just won't switch on that many appliance s. I told him I will wait to hear from should you wish to upgrade as one phase has reached its load limit.
 
Very true unless extension, basements and lofts have been added with electric showers or electric hob and ovens then load can exceed 100a easily I had one property that was tripping due to overload when I explained he required three phase head he was like I don't wanna spend that kind of money. I just won't switch on that many appliance s. I told him I will wait to hear from should you wish to upgrade as one phase has reached its load limit.

What was tripping?
Did you carry out a load study to ascertain exactly what was going on, or how did you assess the magnitude and cause of the overload?
 
What was tripping?
Did you carry out a load study to ascertain exactly what was going on, or how did you assess the magnitude and cause of the overload?
Yes I did go found issue to be extra electric shower added to extension they already had one electric shower. All appliances were fine and tested.
 
Yes I did go found issue to be extra electric shower added to extension they already had one electric shower. All appliances were fine and tested.

I didn't ask if you went there, I asked if you actually carried out some sort of load study. Ie did you connect current recording equipment to the installation to record the actual load?
 

Reply to What are your thoughts on this 3ph domestic. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
995
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
890
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock