Discuss What power rating would this garage door be? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have a roller garage door that my friend has fitted which i've noticed is connected to a socket to give it power, but then has a flood light attached to the control panel which is also connected to the lighting circuit. In other words you need to isolate sockets and lights to make sure the control panel is properly isolated.

I would like to put this garage door on the lighting circuit. I have rang the garage door company and they said that the power was 8W so clearly they have no idea. It is a galvanised door approx 3m x 3m. Direct drive.

Does anyone have a rough idea of what power these types of motors would be?

Cheers in advance :)
 
look on the motor. it should have a rating plate. it will be a FHP motor so will be under 5A, should be OK on the lighting circuit unless the start surge requres a type C breaker.
 
I'm with @Pete999 post #3.
Out of curiosity, what size fuse is in the plug?
You would get one of these that could tell you how much it is drawing?
 
Electrical behaviour and starting load will depend on whether it's an AC or DC motor as both are used, screw or chain drive, and on how well the door is counterweighted. I would expect it to be in the range of 250-500W when running, but would allow 1kW / 5A for starting. Why do you want to run it from the lighting circuit?
 
Electrical behaviour and starting load will depend on whether it's an AC or DC motor as both are used, screw or chain drive, and on how well the door is counterweighted. I would expect it to be in the range of 250-500W when running, but would allow 1kW / 5A for starting. Why do you want to run it from the lighting circuit?
At present the control panel is fed from a socket. In the control panel there are terminals for a light to be wired into it, which it has. This light is also connected to the lighting circuit (so even if the sockets were off the S/L in the control panel could become live if the light was switched on). It would be a right hassle to take the light out of the lighting circuit, so I thought to put the garage door on the lighting circuit so it can be isolated correctly.
 
Are you saying it is energising the light (that is part of the lighting circuit) from the line obtained via the plug, or just that it closes an electrically separate contact in parallel with the light switch to operate the light? The former case is wrong and needs to be fixed as the two circuits are not electrically separate - in theory the plug pins could become live too, from the lighting circuit. If the cable run to the light or switch can have PL and SL connected, then this problem can be solved with a small relay in the panel.

The latter case is electrically fine, merely needs a label on the front identifying the two sources of supply. You would need to isolate the lighting circuit anyway so pulling out the plug is hardly an extra complication. I know it's not so common in domestic situations but in industrial plant it's quite normal to have multiple circuits within a panel.
 
Are you saying it is energising the light (that is part of the lighting circuit) from the line obtained via the plug, or just that it closes an electrically separate contact in parallel with the light switch to operate the light? The former case is wrong and needs to be fixed as the two circuits are not electrically separate - in theory the plug pins could become live too, from the lighting circuit. If the cable run to the light or switch can have PL and SL connected, then this problem can be solved with a small relay in the panel.

The latter case is electrically fine, merely needs a label on the front identifying the two sources of supply. You would need to isolate the lighting circuit anyway so pulling out the plug is hardly an extra complication. I know it's not so common in domestic situations but in industrial plant it's quite normal to have multiple circuits within a panel.
This is what I have Lucien...
garage door.jpeg
 
From what I can make out, you have two supplies at the dp switch. Needs a couple of relays controlling the light, one for manual and one for the sensor, I'd say.
 
That looks very naughty! It's tying the two circuits together and could make the plug live. Where you have a DP switch, replace with one SPST relay with 230V AC coil and 5A rated contacts. Connect the coil to the 'lamp output' from the door opener, and the contacts between the two SL's (lamp direct and via sensor) No wiring alterations needed. Observe electrical separation between the coil circuit and the contacts.

The door opener will however only energise the light when the PIR sensor is also enabled at the 2g switch. If you want the opener to have independent control of the light, you will need to get a PL to the relay from the 2g switch, I don't know if that's adjacent or distant. Optionally bypass the DP switch and put the relay adjacent to the 2g switch.
 
Last edited:
For a light?
 
Hi - sorry to say, but I'd junk all that and attach a small LED fitting directly to the light terminals. That way the 2 circuits remain separate and the new LED light comes on for a timed period as the door opens or closes (guessing at what the board logic is...) :) .
 
Just thinking. Why not just remove the light circuit supply and pick up from the dp switch? 3 wires to the override and sensor if no neutral required.
 
Last edited:

Reply to What power rating would this garage door be? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all hope u all have a fab christmas , my name is Nick and i bought a roller garage door it got delivered yesterday but due to holidays the...
Replies
0
Views
614
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
758
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
893
Hi, I’m new to the forum and am seeking some advice please. I’ve picked up a job that another electrician has abandoned, the job is to...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock