Hi Guys,

I have been asked to install a some lighting & sockets in a lean too come garage come workshop type of thing. I was going to do it in PVC conduit & make a proper job of it rather than surface clip T&E all over the place. I haven't done much in the way of circuit installation using this method, I'm planning to do lights in 1.5mm singles & sockets in 2.5mm. I was thinking of doing the socket radial CPC in 1.5mm, any of you guys do this or would you stick to same size CPC as L&N? Thought as it's a small install, 5 sockets max on 16a MCB it would be a cost effective use of 100m drum of 1.5mm G&Y.
 
Me personally I would stick to the same size as l and n if using singles but I'm sure it would still be OK if you use 1.5 CPC as that's what they use in twin and CPC cable
 
The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
 
Last edited:
lol see above Trev, I only know of that reg due to the 4mm requirement of adding seperate CPCs where not mechanically protected.

The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
 
Last edited:
The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol

Surely 543.1.1 (v) allows the use of 1.5mm² cpc in PVC conduit (which is the case for the OP)?

Certainly for a lighting circuit.
 
Keep reading a bit further down lol

It contradicts itself


Does it? If so, I can't see it.
Surely, you need to read the paragraph as a whole:

If the protective conductor:

(iii) is not an integral part of the cable, or

(iv) is not formed by conduit, ducting or trunking, or

(v) is not contained in an enclosure formed by a wiring system,

the cross-sectional area shall be not less than 2.5mm² copper equivalent if protection against mechanical damage is provided, and 4mm² copper equivalent if mechanical protection is not provided...


ie, if the cpc is in a cable, or in conduit or formed from metallic containment, the 2.5mm² minimum doesn't apply.
 
I would say the opposite applies,

That 2.5mm is the minimum size, however on larger CSA live cables then a smaller csa CPC may be used to a minimum of 2.5mm subject to adiabatic etc. subject to the other conditions of that reg.

Besides the smallest size I stock is 2.5mm (smiley)

Agree about metallic containment btw.

Edit: that is what I meant about "typical bloody regs", it is either minimum 2.5mm with mechanical protection or it is contradictory by allowing a smaller size in containment (which is mechanical protection),lol
 
Last edited:
Hi,
Wired a small workshop a while ago for a friend, did all the rings and lighting in 2.5 singles; one size no messing about with different sizes or running out of this or that.

Regards.
 
The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
Why do they make 1.5mm2 Green and yellow then?
 

Reply to What size your CPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi there, We're currently having a new kitchen fitted and in the process we've had some new electrical work done. The electricains are comeing...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock