The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol

Surely 543.1.1 (v) allows the use of 1.5mm² cpc in PVC conduit (which is the case for the OP)?

Certainly for a lighting circuit.
 
Keep reading a bit further down lol

It contradicts itself


Does it? If so, I can't see it.
Surely, you need to read the paragraph as a whole:

If the protective conductor:

(iii) is not an integral part of the cable, or

(iv) is not formed by conduit, ducting or trunking, or

(v) is not contained in an enclosure formed by a wiring system,

the cross-sectional area shall be not less than 2.5mm² copper equivalent if protection against mechanical damage is provided, and 4mm² copper equivalent if mechanical protection is not provided...


ie, if the cpc is in a cable, or in conduit or formed from metallic containment, the 2.5mm² minimum doesn't apply.
 
I would say the opposite applies,

That 2.5mm is the minimum size, however on larger CSA live cables then a smaller csa CPC may be used to a minimum of 2.5mm subject to adiabatic etc. subject to the other conditions of that reg.

Besides the smallest size I stock is 2.5mm (smiley)

Agree about metallic containment btw.

Edit: that is what I meant about "typical bloody regs", it is either minimum 2.5mm with mechanical protection or it is contradictory by allowing a smaller size in containment (which is mechanical protection),lol
 
Last edited:
Hi,
Wired a small workshop a while ago for a friend, did all the rings and lighting in 2.5 singles; one size no messing about with different sizes or running out of this or that.

Regards.
 
The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
Why do they make 1.5mm2 Green and yellow then?
 

Reply to What size your CPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
231
Hi all, Was wondering if you could help please. I'm looking to fit a BG IP66 external socket mainly for occasional jet wash/vacuum usage and...
Replies
9
Views
1K
The customer has suggested from a previous electrician that the oven requires a new circuit installed . Upon viewing the instructions it is stated...
Replies
6
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock