Hi Guys,

I have been asked to install a some lighting & sockets in a lean too come garage come workshop type of thing. I was going to do it in PVC conduit & make a proper job of it rather than surface clip T&E all over the place. I haven't done much in the way of circuit installation using this method, I'm planning to do lights in 1.5mm singles & sockets in 2.5mm. I was thinking of doing the socket radial CPC in 1.5mm, any of you guys do this or would you stick to same size CPC as L&N? Thought as it's a small install, 5 sockets max on 16a MCB it would be a cost effective use of 100m drum of 1.5mm G&Y.
 
Me personally I would stick to the same size as l and n if using singles but I'm sure it would still be OK if you use 1.5 CPC as that's what they use in twin and CPC cable
 
The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
 
Last edited:
lol see above Trev, I only know of that reg due to the 4mm requirement of adding seperate CPCs where not mechanically protected.

The smallest size of a CPC if not an integral part of a cable is 2.5mm, I will look the reg up in a while.


edit: reg number 543.1.1, but there may be an exception see part (V) of that reg, there is a bit of a contradiction as below that it states that it shall be no less than 2.5mm if mechanically protected.

Typical bloody regs, lol
 
Last edited:

Reply to What size your CPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
232
Hi all, Was wondering if you could help please. I'm looking to fit a BG IP66 external socket mainly for occasional jet wash/vacuum usage and...
Replies
9
Views
1K
The customer has suggested from a previous electrician that the oven requires a new circuit installed . Upon viewing the instructions it is stated...
Replies
6
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock