The BS EN will be 61008 and the type will be AC.

They types are -

A = Protection against AC earth fault currents containing pulsating DC components
B = Protection against DC earth fault currents
AC = Protection against AC earth fault currents
S = Delayed
 
Where is this field? Do you mean on the schedule of test results? If so, the BS EN field is for overcurrent device, not RCD!
If being used as a main switch, then just put down BSEN 61008-1. The RCD "type" is irrelevant, just put a dash!
 
Yes but the over current device just require type and In, The BS number will be required on the EIC which can either be put in the characteristic of the supply and earth section or Main Switch or Circuit Breaker section, where the RCD would be noted if it is used main circuit breaker.
 

Reply to What type is this RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Given the RCD pictured below With the manufacturers instructions here: Am i right in interpreting that as well as being able to bring the...
Replies
4
Views
395
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
663
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
281
i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
825
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock