Good morning all

First time posting so quick introduction
I'm John I'm employed by my.local council To carry out EICR'S

I've been in this job now for around 3 month every house I have tested has been rewired or partially rewired in the last 10 years or so

Now about the C3 and maybe this is just me because its a massive pet hate of mine

Every single CU I have looked at has the MCBS ranging from lowest to highest from the RCD for example

RCD 6A 6A 16A 32A

So I see this as a C3 as I was always taught and have always done it from highest to lowest from the RCD

My boss today asked why I C3 this as it's not a big deal

as I believe it's is the testers discretion as to what goes down on the coding and I this is something would never do

Again silly to most people I know but to me it's wrong

What's your thoughts and opinions on this ?

Thanks your friendly neighborhood tester John :)
 
Welcome to the forum, In answer to your question I would question where in the regulations it says you have to order the ratings in any particular way?
What do you think are the consequences of not doing so?

If you call testers discretion then you still have to give good reasoning for your discretion and you should be able to back it up with a regulation or some other form of evidence.
 
As said above, an EICR is carried out using the requirements of BS7671 as the standard for the inspection.
If you felt that a busbar or any equipment was being used past the rating it was designed for then that would be a safety concern, but obviously the order of devices would not alter this situation.
 
Thanks for your reply chaps and I totally agree there is no reg which requires this and it would not alter the installation at all it was just something I had drummed into me from being an apprentice and generally thought it was a rule of thumb when installing a CU as I stand corrected lol I will no longer C3 it again it was just something i was taught to always do
 
As above. There is no regulation so there is no "C anything" to report as you could not note in your EICR which regulation has been breached.

In the old days it was the habit to put the fuses in descending order, probably because there wasn't so much copper in the live distribution bar. But not a regulation, even then.
 
I agree we were always taught that the highest load circuit was nearer the main switch
When I think about it we maybe just accepted most of what we were taught without questioning why it was the case

As stated there is no justification for the order of the circuits to be coded
As far as a inspector making judgement,its always a good point to remember that each time we code,we should be able to reference a regulation to back up our decision
 
Everyone has their ways of doing things on jobs, but like what has been said - if you can’t quote a regulation it contravenes then you certainly can’t code it.

I always put high to low from main switch or RCD.
 
If you read the manufacturers instructions they recommend mixing heavy and light loads to avoid mutual heating and magnetic influence so having the MCBs in ascending or descending order would potentially be against manufacturers instructions.

So you're all wrong!!! ;)
 
was common back in the 70's to put the highest loads closer to the main switch, the idea being that the highest busbar loading would be the shortest, but it was never a reg.... another old wives tale. like bonding metal windows.
 

Reply to Whats your opinions Would you C3 it ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
2
Views
481
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock