Hi hope someone can help, i need to record the protective device on a MWC and not sure which to enter.

I have removed an old bathroom heater on a 20A radial and rerouted cabling to feed an RCD FCU, the load side of which feeds into the bathroom serving towel rail with a local DP (20A) switch.

On the MWC for protective device, should I enter the 20A fuse serving the entire circuit, or the 3A 1361 within the RCD; or should I write out two seperate certs for each leg. Thanks
 
Alright looking at this this way, say hypothetically an fcu is fitted to 2.5mm ring (protected by 32A c/b), the load side of the 13A FCU supplying some equipment is in 1.5mm.

So for above scenario the MWC protective device would still be the 32A c/b ?
 
Either/or as Murdoch beat me to it if putting on one MWC state towel rail protected by local RCD protected switched fused spur with 3A BS1361 fuse.
 
The minor works certificate asks for the protective device for the modified circuit so why bother mentioning the bs 1362 fuse as it's the mcb in the consumer unit it's concerned with?
You can make a note as already suggested say via a 3amp FCU
 
But the fuse and FCU is a part of the modification, why not cover yourself with a little extra detail.
Yeah I would always state tho the device in the consumer unit as the over current protective device.
In comments I would say something like
External light installed via fused connection unit fitted with 3 amp fuse from say down stairs ring final circuit.
 
As a side note do any people write down the ring continuity results if say spuring a double socket from local ring final circuit in the comments section?
 
I'd just record the Zs in that example, in reality that would almost always be a low cost job and you wouldn't be allowing the time for end to end testing.
Do you not confirm that the ring is actually a ring and that adding a extra socket brings a final of overloading part of the circuit as it's discontinuous?
I record it just to cover my self really
 
Generally the Zs reading would tell you a lot about that Ian but I'd check both ends were live at the point I was taking the spur from while disconnected.
 
Do you not confirm that the ring is actually a ring and that adding a extra socket brings a final of overloading part of the circuit as it's discontinuous?
I record it just to cover my self really
If I work on a ring final I always note the continuity readings.
 
Generally the Zs reading would tell you a lot about that Ian but I'd check both ends were live at the point I was taking the spur from while disconnected.
What disconnect the ring, liven it up and see if both ends show voltage.
 
As a side note do any people write down the ring continuity results if say spuring a double socket from local ring final circuit in the comments section?

I record continuity readings in notes in MW. In fact I test for such before starting my addition. Always have my fingers crossed when doing so, you never know whether the DIY'er been there before you :)

Edit; That said, never checked the RFC if spurred from the origin at the CU.
 
Last edited:

Reply to Which Protective device on MWC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock