Discuss Which Starter Contactor in the UK Electrical Forum area at ElectriciansForums.net

Has it only just started doing this or did it previously carry on running once the start button was released.
 
Has it only just started doing this or did it previously carry on running once the start button was released.
No this is how it should run for safety. The whole thing got ripped out before I got to it. So starting on the back foot. I've got a new motor but need to get a starter contactor. There is a separate button to run the motor, not on the contactor.
 
Lads on the comp so i cant check regs.
Dont you need a thermal overload for a 3hp motor?
 
upload_2018-12-9_20-8-16.png
 
Just got the paperwork out for the motor and it has an overload built in .
Can you post this paperwork?
Do you have the full load current of the motor?
Also what does this motor drive as this may affect the duty rating of the contactor and also may determine if a safety circuit may need to be incorporated.
 
I take it this is a deadmans operation method, you just need a suitably rated starter that you can remove the retaining link wire out of the circuit to give this operation method, the majority of motor DOL starters out there allow you to do this, as mentioned though you will need overload protection fitted, I also would like to see this paperwork for the motor, motors can come with integral thermal devices but they normally require external monitoring but this alone may not satisfy the requirements for overload detection as they are usually a secondary backup as motors can overheat without running in overload.
You are the designer of the control circuit regardless if your copying the old method therefore you should be complying to BS 60204 (2018), this falls outside of the BS7671 although you do find the odd relevant regulation that is reflected in the BS7671.
 
You will have to install a stop button and change the wiring in the control circuit if you want it to latch on.
Only if it is safe to wire it like that.

The OP wants it to run as it is now, hold to run (or dead mans switch)
 

Reply to Which Starter Contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
473
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
993
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I have a sawbench motor that needs an on/emergency off switch fitted, have the hylec on/off switch and a contractor 240V coil with NC contacts...
Replies
0
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock