Discuss Who need cpc continuity? in the UK Electrical Forum area at ElectriciansForums.net

KeithC

-
Reaction score
13
Was helping a fiend to change some socket outlets, standard white to brushed steel in her kitchen. She only had the house re wired 2 years ago - got the part P paperwork.
This is what we found behind one socket. WTF was the bloke thinking??
Also obviously doesn't bother with grommets.
I also had a look at putting an extra light point to her landing, just by the loft hatch I found a junction box with 5 1.5 t&e going in, a little surprised to find that on a new install. On opening I found a mixture of brown/blue AND red/black!! Obviously there wasn't even a warning on the CCU.
sorry the pic is rotating through 90 degrees, don't know how to change
 

Attachments

  • image.jpg
    177.4 KB · Views: 69
So what your saying is the cpcs weren't connected to the earth term on the socket? Or were they connected to that connector and pig tailed to the socket earth term? Or no pig tail to the socket?

Did they leave a test schedule at the board or anywhere else? Maybe they just sat in the van and made up the readings.

Typical competetive priced rewire, or poor old customer taken in by the usual pikey fannying.
 
So what your saying is the cpcs weren't connected to the earth term on the socket? Or were they connected to that connector and pig tailed to the socket earth term? Or no pig tail to the socket?

Did they leave a test schedule at the board or anywhere else? Maybe they just sat in the van and made up the readings.

Typical competetive priced rewire, or poor old customer taken in by the usual pikey fannying.

One was in the earth terminal on the back of the socket outlet, the other was floating just like that in the choccy block. There was no paper work at all by the CCU.
 

Reply to Who need cpc continuity? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning - just a photo for info to show what's out there (as if most don't already know!!!) & to reiterate the ignorance of some householders. A...
Replies
32
Views
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
Replies
30
Views
10K
Visited my mates place tonight as moved to a new property 2 yrs ago, starts going through the rooms, and wisely leaves the elec alone ! Find a...
Replies
6
Views
1K
Good Evening all, Been at a property today starting intial tests for a board change tommorow. There are two ring circuits, on one of the ring...
Replies
21
Views
4K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top