I removed a fuse and before reinserting did the following tests using test lamps. Live side - Neutral = 230V, Dead side - Neutral = 0V, Live side - Dead side = 0V.
I then used a multimeter to check these results as I was expecting a potential difference of 230V between Supply side and dead side.
I got Live side - Neutral = 230V, Dead side - Neutral = 15V, Live side - Dead side = 230V.
Why did I get 0V Live side - dead side using test lamps, but get the expected 230V when using a multimeter?
 
You don’t test between the two sockets of a fuse.

Doing this with a load on the circuit passes the current through your test device as if it was part of the circuit.
 
This was revealing the difference in sensitivity and input resistance between the multimeter and the test lamp. When connected between live and dead side of tbe fuse, the test device is in series with the load forming a voltage divider. The fraction of the total 230V supply that the test device sees depends on the ratio of its resistance to the total.

The test lamp had a much lower resistance than the load (at the moment of test) and saw negligible voltage, i.e. most of the 230V existed across the load and the stray capacitance of the circuit. The multimeter had a much higher resistance and saw effectively all of the 230V, with hardly any of it dropped across the load.

Then with the multimeter connected Load - N, even the stray current on the circuit induced presumably from other live circuits nearby, was sufficient to register 15V. The test lamp's low resistance shunted this without registering any visible reading.
 

Reply to Why did test lamps show 0V between live side and dead side? in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock