Discuss Why does new 1700 watt microwave keep burning out my 20amp dedicated breaker? in the USA Electrical Forum area at ElectriciansForums.net
Broken, kaput, no longer works. No visible damage, just a broken breaker. New breaker works for a bit then also stops working. Doesn’t trip, just breaks.What do you mean by burning out.
Nothing visible. But I didn’t open up the breaker to look inside.Can you post a photo of the damage?
120. Psuedo professional electrician told me I need to run a 10 gauge wire to the box. But I assume 12 would do it. What else could it be? The outlet stops working even though the breaker is still switched on. Sensor pen tells me there’s still some electricity flowing but not enough for a light.is the microwave on 120V or 240V?
First, thank you for your time everyone, I appreciate it. Copper wire, newer box, old 1200w microwave was connected to a15amp outlet and same 20 amp breaker for several years. After installing new microwave it stops drawing power after a few cooks. I replaced the outlet to a 20 amp and still nothing. I replaced the breaker and it worked again. Until the same thing happened a couple days later. Breaker and everything is solidly connected. As an ametuer I don’t have the testing equip or knowledge about breaker to see if it still works. There is one other thing I did and that was run another 5 foot wire off the outlet for the gas range below to plug into. (Just for clock, spark and timer) However, nothing was plugged into it or drawing extra power both times it went out. Should I try a gfi outlet? I don’t know how to get it working again other than installing another (3rd)new breaker.Breakers don't usually stop working due to overload because that's what they are there to protect against. They should trip before being damaged. Therefore I agree with @westward10 that the first breaker might actually still be OK but was not making good contact with the busbar in the panel. Replacing the breaker re-made the contact for a while, and now it has gone open-circuit again, or some similar explanation other than the breaker itself. Or, the breakers are faulty (are they from the same source / batch?)
In this scenario the non-contact sensor is not the best tool for tracing as it may not clearly show the difference between a genuinely hot wire and one that is floating. However, if with the breaker and oven both switched on and the outlet apparently dead, just check whether it lights on both the hot and neutral of the circuit, because if it does that clearly points to a bad neutral connection at the panel which you might not have checked yet.
I would check the breakers away from the panel with a continuity tester as this will prove quickly whether there is a circuit through either or both of them, without relying on the contact through the panel busbar.
The #10 wiring thing seems to be a red herring. If the circuit is very long then #10 might be needed for optimum voltage at the outlet, but it shouldn't in any way affect the breaker. This is new, copper wiring yes? Not a re-used old aluminum circuit?
How old is your panel is it the Stab-Lok style, can you show a pic.
clips on. Put the old one back on, still doesn’t work, put a new one in, works. But I’m not going to run the microwave yet.Installing another breaker is not the way forward. Does the breaker screw to the busbars or does it just clip onto them.
Can you tell me exactly the testing equipment I need and what I should test? Am I just testing the breaker? 2 breakers have stopped working. They don’t work when I put them back in. A 3rd new breaker works again but I don’t want to run the microwave until I can figure this out.You could lose a lot of time on trial-and-error swapping out of parts. It really does make sense to test, or get someone else to test, where the problem is. If for example it is the contact between the breaker and the panel busbar that is intermittent, swapping it will probably make it work again briefly, but so would putting the original one back. WIth proper test equipment it should be possible to nail this in a few minutes.
Great idea. I switched both the breakers and the wires. The breaker I thought was broken does work with another wire both in the same place and different place. The microwave wire isn’t working in any breaker at any place. So it’s not the breaker I’m concluding. Even though the outlet doesn’t work I’m still getting a a strong electrical reading from the outlet. I removed the outlet and tried swapped it in a different place and it works. So it’s not the outlet. Am I right to conclude this is a wire problem? I’ve got to crawl into the attic and take a look to make sure it’ looks goodThat is Square D QO. Have you tried the breaker in a different position or temporarily connect to another 20A breaker, don't move it just connect your wire to another breaker.
Just got out of the attic. Found the 12 gauge from the box was wired to a14 gauge extension wire up there. The wire nut on the white wire was melted. My idea is to continue a12 gauge extension all the way to the outlet (5 feet). Otherwise, does this wiring look good? I’m running another receptacle off of the dedicated microwave box below it to plug in the gas oven which draws a trickle for sparks, light and timer.Is the microwave outlet the only accessory on this circuit.
Thanks for your time. I don’t understand most of it. As you can see in my recent reply with photos, the nut was melted where it connected to an extension in the attic. They ran a 14 off a 12, so I’m going to replace it with a 12 in a box. But very odd that changing the breaker would have solved this problem the first time. I agree this microwave draws a lot of power. Lmk if you think 20amp breaker and outlet are still sufficient.First a question for the OP please? How far in metres or yards is your breaker board from the supply transformer? If your supply is overhead you ought to be able to see a round drum like object to which your supply cables connect to.
====================================================================
Now to my learned colleagues. I have taken literally what the OP has said - the mcb has burned out - so it may well be the microwave oven is faulty in some way - but I suspect not since it is new. Anyway, it seems to me this MWO is a powerful model - 1700W. The Panasonic we had before disposing of it was only circa 800W.
The way the high voltage is generated for the magnetron is something like a step-up isolating transformer, capacitor C1, charging/swing diode D1 see:
https://www.researchgate.net/figure...in-a-microwave-oven-The-switch_fig1_234930316
When energised with HV the magnetron is pulsed on/off at to produce bursts of microwave radiation with a repetition rate equal to the mains frequency 50/60Hz.
Such a circuit will produce a primary current waveform which is not sinusoidal since the diode conducts on one half of the cycle and the magnetron on the other - once there is sufficient applied emf for forward biasing of the diode and circular thermionic conduction in the magnetron. You get the gist.
Such a power supply has a low power factor - I'd guess 0.65. Thus for a 1700W real power output the apparent power is 1700/0.65 = 2600VA If the supply voltage is 120V then the rms current is 2600/120 = 22A when the MWO is operated continuously at 1700W. I doubt this happens since it would quickly turn the contents of the oven to burning carbon. The magnetron's HV will be further pulsed on and off to achieve a lower average cooking power. But for the on periods the current will be circa 20 -22A - the continuous average rating of the breaker.
The cycling on and off of the magnetron is normally done on the primary side of the transformer by crudely switching the supply. No switching to minimise transients then - unless the MWO uses an appropriate solid state switch. The transient current for such a transformer rectifier combination can be up to 10, maybe 20 times the steady state current with a decay dependent on the L/R time constant.
The current waveform will have a high crest factor - the ratio of peak current to rms current - greater than the usual purely resistive (PF=1) circuits sinewave crest factor of 1.414. And because of what I said in red above will be of short duration something like this:
https://www.researchgate.net/figure...orms-in-a-Typical-Peak-Rectifier_fig1_3627656
I wonder whether then the Square D QO 20 A breaker has unsuitable overcurrent/short circuit characteristics and contact type to pass the peaky high current short duration waveform causing the magnetic trip to operate though I think the OP suggests this has not happened since the lever does not move.
Instead the contacts burn out because they are subject to a current density far higher than they are able to cope with - resulting in gradually and eventually catastrophic failure - they burn out. The Joule/Ohmic heating of these contacts depends on a square law which rises very rapidly with increasing current I/current density J eg: I/Isq = 20/400, 21/441, 25/625, 30/900, 100/10000, 200/40000. These very high peak currents albeit of short duration can cause very high local heating of the contacts. And small contacts will suffer most.....
Interestingly, thanks to Westward10's identification of the breaker as type QO, there is a specialist range of QO breakers viz QO - HM and QO -HID to handle one off switch on surge currents and cyclical surge currents respectively. See page 8 of:
https://download.schneider-electric.com/files?p_Doc_Ref=0730CT9801
QO® and QOB Miniature Circuit Breakers Special Application Circuit Breakers 8 07/2008
QO-HM and QOB-HM High Magnetic Circuit Breakers QO-HM and QOB-HM high-magnetic circuit breakers are recommended for area lighting (such as athletic fields, parking lots, and outdoor signs), when using lamps of inherent high inrush current, individual dimmer applications or other applications where high inrush currents exceed standard tripping conditions. These circuit breakers are available in one-pole 15 and 20 A ratings only. QO-HM and QOB-HM circuit breakers are physically interchangeable with standard QO and QOB circuit breakers and accommodate the complete range of QO accessories. QO-HM and QOB-HM circuit breakers are manufactured with the magnetic trip point calibrated at a much higher level than standard QO and QOB circuit beakers, as shown in Table 3.
QO-HID and QOB-HID High Intensity Discharge Circuit Breakers QO-HID and QOB-HID circuit breakers are for use in high intensity discharge (HID) lighting systems, such as systems using mercury vapor, metal halide or high-pressure sodium lighting units. These circuit breakers are designed to handle the high inductive loads, harmonic currents and cycling which are inherent in HID lighting systems. QO-HID and QOB-HID circuit breakers are physically interchangeable with standard QO circuit breakers and accommodate the complete range of QO accessories. QO-HID and QOB-HID circuit breakers are manufactured with larger contacts than standard QO and QOB circuit breakers to allow switching of high inductive loads. They also have magnetic characteristics similar to QO-HM and QOB-HM high-magnetic circuit breakers to allow the circuit breaker to hold in against the high starting inrush currents which are typical in HID lighting systems.
Or something along these lines... ?
====================================================================
For the OP - I am providing no advice just yet on what to do.
Oh, and the breaker box is about 15 meters from the transformerThanks for your time. I don’t understand most of it. As you can see in my recent reply with photos, the nut was melted where it connected to an extension in the attic. They ran a 14 off a 12, so I’m going to replace it with a 12 in a box. But very odd that changing the breaker would have solved this problem the first time. I agree this microwave draws a lot of power. Lmk if you think 20amp breaker and outlet are still sufficient.
Just got out of the attic. Found the 12 gauge from the box was wired to a14 gauge extension wire up there. The wire nut on the white wire was melted.
My idea is to continue a12 gauge extension all the way to the outlet (5 feet). Otherwise, does this wiring look good? I’m running another receptacle off of the dedicated microwave box below it to plug in the gas oven which draws a trickle for sparks, light and timer.
Sorry for stepping on Megawatt’s toes but this photo seems odd/wrong but that may be because of the angle it was taken from. Why are the Black and white of one cable connected to white and black respectively of the other cable causing the hot and neutral to be reversed?Just got out of the attic. Found the 12 gauge from the box was wired to a14 gauge extension wire up there. The wire nut on the white wire was melted. My idea is to continue a12 gauge extension all the way to the outlet (5 feet). Otherwise, does this wiring look good? I’m running another receptacle off of the dedicated microwave box below it to plug in the gas oven which draws a trickle for sparks, light and timer. View attachment 88404
Optical illusion. There were connected correctlySorry for stepping on Megawatt’s toes but this photo seems odd/wrong but that may be because of the angle it was taken from. Why are the Black and white of one cable connected to white and black respectively of the other cable causing the hot and neutral to be reversed?
Oh my gosh I’ve found all sorts of lazy shortcuts and cheapness in this house. Our basement fluorescent lights were “plugged in” to outlets hidden above the drop ceiling. The black and white wires were just shoved into the slots if the receptacle. Amazing.Nice to see whoever fitted that joint was so lazy they couldn't even be bothered to cut the stripped back sheathing off.
It did turn black. What I’m not clear about is if it had something to do with 12 gauge connecting to a 14 gauge and overheating with the amount of power the microwave was drawing, or if when I remodeled and reset the box the wire in the attic moved and pulled out of the nut just slightly? Either way, it doesn’t explain why replacing the breaker worked-/at least until it didn’t. After running another 12 gauge off the wire to the microwave yesterday, everything seems to be working normally now. I’ve even got the gas stove plugged in to it. Hope it stays this way, and I’m using the breaker I thought was broken. Thanks so much for your help and I’ll reply again if there are further issues.One connector, the black is hard to see but I believe the two whites are together it's just that one is burnt black.
What your problem was it wasn’t as much as the wire splicing from 14 to 12. We have dumb a— people who do electrical work and as stated above the jacket wasn’t skinned back enough to even make a decent splice, the NEC requires 6 inches of wire extended out of the box. The second thing is wire nuts work if these idiots would tighten them up correctly you wouldn’t have no problem. Your breaker done it’s job, it was tripping because where the splice was made you had one arching which was more than likely arched to the to the neutral. When I splice with wire nuts I get them so tight the wires start twisting up. After that tape up each spliceIt did turn black. What I’m not clear about is if it had something to do with 12 gauge connecting to a 14 gauge and overheating with the amount of power the microwave was drawing, or if when I remodeled and reset the box the wire in the attic moved and pulled out of the nut just slightly? Either way, it doesn’t explain why replacing the breaker worked-/at least until it didn’t. After running another 12 gauge off the wire to the microwave yesterday, everything seems to be working normally now. I’ve even got the gas stove plugged in to it. Hope it stays this way, and I’m using the breaker I thought was broken. Thanks so much for your help and I’ll reply again if there are further issues.
Sensor pen tells me there’s still some electricity flowing but not enough for a light.
...with the breaker and oven both switched on and the outlet apparently dead, just check whether it lights on both the hot and neutral of the circuit, because if it does that clearly points to a bad neutral connection...
Reply to Why does new 1700 watt microwave keep burning out my 20amp dedicated breaker? in the USA Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.