Discuss Why Earth before IR testing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Woofie

-
Reaction score
3
A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?
 
Because the IR test is between line and CPC/earth - if the CPC isn't connected to anything then you could have a short between line and CPC/earth which the test wouldn't identify.
 
By completing the R1+R2 testing at each point on the circuit during initial verification you are confirming the cpc is continuous and present then you can move on to IR testing , assured that the cpc’s will be included in the test and is not discontinued to give the tester false or incorrect readings.
There is a reason that the testing sequence in initial verification is there and it’s worth remembering that any issues found during IR may mean you have to repeat the previous tests.
 
When you say the cpc / armour connected to earth are you just referring to swa cables and how would it not be connected to earth if glanded to a metal enclosure.
 
It has been explained but you don't seem to have understood.

You have to have a CPC for the IR test to work.
You need to test the CPC before you do any other test that needs the CPC.

It's like making sure your tester works and your leads aren't broken before you start testing.
 
It's the same idea - if the live is making contact with the armour then an IR test will show that up unless the armour isn't earthed, in which case it'll just liven up the armour to 500v. The test might show you have a high resistance, but then when you energise the circuit the armour will become live.
 
Perhaps the op is getting a little confused and is referring to the requirement to discharge the conductors of an swa to earth following an insulation resistance test. I could be barking up the wrong tree though.
 
Too right I'm confused. The question isn't specifically about SWA but taking that as an example, if there were a phase to armour fault that would be picked up even if the armour were not connected to earth.
 
When you say the cpc / armour connected to earth are you just referring to swa cables and how would it not be connected to earth if glanded to a metal enclosure.
Might not be a very good termination, judging by some I have seen,
 
However if there was a fault from a live conductor to another piece or earthed metal nearby the test from armour to live conductor woudl show as OK.
If the armour was connected to the earthing system then the short would be shown on the test result.

View attachment 41916
excellent explanation.
 

Reply to Why Earth before IR testing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
745
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
654
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
568
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
523
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock