Discuss Will my garage handle my planned usage? in the UK Electrical Forum area at ElectriciansForums.net

LHensh

DIY
Reaction score
0
Hi,

Just looking to get some advice before I get too carried away with plans for using my garage as a home office/ManCave.

The garage has an old fusebox (photo attached) with 15amp and 5amp fuses which is fed by a 2.5mm cable coming from the house.
The feed to the garage comes from the main consumer unit in the house.

I'm trying to work out if my expected maximum power consumption could be safely handled by both fuses.

Sockets:

Oil filled radiator (photo attached) 1000w @ 240v = 4.17A
Router = <0.5A
TV = <0.5A
Beer Fridge = 0.75A
Coffee Machine = 5.5A
Laptop = <0.5A
Monitor = <0.5A
Projector = 1.9A
LED strip lights =<0.5A

Total Amps = 14.8

Lights:
10x LED downlights 5W X 10 X 240V = 0.21A
2x LED outside lights (4 bulbs) 5.5W X 240V = 0.09A

Total Amps = 0.3

For the sockets, assuming that all of the lower usage appliances all run at 0.5A and are all running at the same time (which wouldn't be the case) I should be within the 15A limit.

Lights are no concern as would be well under the limit.

Am I on the right lines here?
 

Attachments

  • PXL_20220120_194900551.jpg
    587.9 KB · Views: 24
  • PXL_20220120_194929262.jpg
    240.1 KB · Views: 23
Exactly as @littlespark said. Main questions being:
What is the circuit breaker rating for the garage circuit in the house? A photo of this consumer unit would help.
Is this an RCD protected circuit?
What is rough length of circuit?

My gut reaction is that this will probably be ok from a loading point of view as the heater, coffee machine, and fridge will cycle on thermostats. While you wouldn't do it like this if starting again, subject to answers above it should meet the needs.

My advice is to pay a sparks for 2 or 3 hours to IR test the current wiring garage supply, confirm the total earth loop impendence (making sure it will trip the house breaker in fault conditions), and stick a modern garage consumer unit in. It's not a big job.
(You'd also get an installation certificate and building control notification certificate which helps if you ever sell the house.)
 
The 2.5mm cable from house could carry 20A depending on installation method… One issue is what is feeding this 2.5mm cable and distance between house and garage.

It should be rcd protected, and if not… the board in the garage needs to incorporate rcd protection.
Yeah the board in the house is RCD protected. May well have someone replace the fuse board with something a bit more up to date. Not sure if they'd put a second RCD on the garage end or of that would be counter intuitive?

Hard to say the length of cable run from house to garage as it not clear where/how it runs, but I expect it will be 10-15 metres
 
There is no benefit of having 2 x RCDs,one at source and one at garage… If there’s one at source already, that’s fine.
The cable feeding the garage may demand it anyway.

The sub main fuse board in the garage needs replaced though.
 
My advice is to pay a sparks for 2 or 3 hours to IR test the current wiring garage supply, confirm the total earth loop impendence (making sure it will trip the house breaker in fault conditions), and stick a modern garage consumer unit in. It's not a big job.
(You'd also get an installation certificate and building control notification certificate which helps if you ever sell the house.)
Thanks, this is exactly what I was thinking/hoping would be the case.

I have attached pictures of the board. The garage supply runs off the far right breaker which is also used for the kitchen sockets.

From there it runs to a module faceplate (not sure on correct term) which has a switch dedicated to the garage supply.
 

Attachments

  • PXL_20220121_093928257.jpg
    312.8 KB · Views: 20
  • PXL_20220121_095011673.jpg
    225.2 KB · Views: 19
Yes… that’s more of an issue. It’s now a spur from an ring final circuit and not a radial from source.

Quite a lot of high power items from that one switch bank already.
 
Is there an easy route from your consumer unit to the garage? I'm thinking probably not and that's why the feed was taken from the ktichen grid switch.
 
Unfortunately no easy route to the garage from the consumer unit.

How much of an issue would it be having my planned usage run through the setup as it stands?
 

Reply to Will my garage handle my planned usage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
I
Hi everyone. Found you guys through Google and can see this a good site. So I'm hoping some of you can answer some questions for me regarding the...
Replies
6
Views
2K
S
Hello Guys, I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all...
Replies
21
Views
14K
RISElectrical
R

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock