Discuss Wiring a kitchen and where you put appliance sockets in the UK Electrical Forum area at ElectriciansForums.net

I go back to previous post, not next door :D but next adjacent floor unit or wall unit; there's no sufficient space behind any appliance for plug & socket without it standing proud (someone will make something of standing proud!)
 
Sorry but if I was customer spending anywhere from 5k to 15k to 55k [Northern Ireland Price range, add on about 25-35% for Mainland) on a good new kitchen....there is simply no way I'd be happy with holes drilled for plugs to come through units and for sockets to be stuck inside units.
 
Simply because people are advocating concealing sockets behind built on appliances, or loose behind kick boards.
A kick board is easily removed (unlike an integrated appliance). It can be removed in seconds. I'd call that very accessible.

Is fitting a click flow connector to a bit of floating T&E really acceptable (post #8). I wouldn't be too happy with it ... flex outlet plate a better job, but neither are MF rated. But what you have installed needs to be accessible as well anyway??

Bit of pot-kettle-black there.
 
Simply because people are advocating concealing sockets behind built on appliances, or loose behind kick boards.

To add to the clouds in this thread,sockets are very often sited in adjacent cupboards
We can read the Iee Building regs guide and 5.2.2 of that guide specifically mentions not putting sockets in cupboards
They make the statement then use the word "should" be mounted on the fabric of the building and not in kitchen cupboards

If the intention is use only the fabric of the building why didn't they use the word "must"!

The Iee can sometimes speak with forked tongue :)
 
To add to the clouds in this thread,sockets are very often sited in adjacent cupboards
We can read the Iee Building regs guide and 5.2.2 of that guide specifically mentions not putting sockets in cupboards
They make the statement then use the word "should" be mounted on the fabric of the building and not in kitchen cupboards

If the intention is use only the fabric of the building why didn't they use the word "must"!

The Iee can sometimes speak with forked tongue :)
Trouble is the UK has 4 sets of building regs. And seem's like even the guides on them can't give a straight answer.

I have no issue with a socket mounting inside a unit regs/safety wise. I just think it looks terrible and like a botch job, and the kitchen carcass will have taken a bit of butchering works to have it done...especially if a hole is drilled for plug
 
Sausage fingers its late floating, ana raised no kick boards required and they look like rubbish.
I don't mind kickboard's, do like floating kitchens though, they seem to be becoming more the norm in the high end ones.
 
A kick board is easily removed (unlike an integrated appliance). It can be removed in seconds. I'd call that very accessible.

Is fitting a click flow connector to a bit of floating T&E really acceptable (post #8). I wouldn't be too happy with it ... flex outlet plate a better job, but neither are MF rated. But what you have installed needs to be accessible as well anyway??

Bit of pot-kettle-black there.

In answer to the click flow, well my answer is that there isn't a fuse in it, a flex outlet plate - maybe but the depths of the units made it tight, plus the supplied leads were so short.

As for the MF - does a connection behind an appliance need to be MF? A plug and socket isn't MF, an outlet plate isn't MF. in fact, no connection that could be undone is really MF.

I had to dismantle part of a kitchen recently to replace a fuse in a plug for a cooker hood - the client wasn't very happy about the bill - but she wanted the hood working!

As for the regs about kitchen cupboards not being the fabric of the building - hum - so are they advoccating a large hole in the back of the cupboard for a plug to go into the wall?
 
I have in the past, put a socket behind a built in appliance, with DP switch above (my own kitchen). I wouldn't do so now, simply because if the fuse in the plug top goes, there's a certain amount of dismantling of the kitchen unit & appliance to access said plug top. I know, because I've had to do so in my own kitchen :mad:.

I now install with DP above worktop & socket in adjacent cupboard, or as some customers prefer, just socket in adjacent cupboard.

As regards the advice from building regs, about not putting sockets on or in kitchen units, what advice do they give about under cupboard lighting, and Mrs Miggans and her socket for her mixer on her island unit :)
 
I have no issue with a socket mounting inside a unit regs/safety wise. I just think it looks terrible and like a botch job, and the kitchen carcass will have taken a bit of butchering works to have it done...especially if a hole is drilled for plug

Can't criticise you, if you feel that sockets should be mounted behind appliance or behind kickboards, whatever is practicable for you & your customer(s).

As regards not cutting holes in units, can't see how you get away without doing so for water supplies to dishwashers, washing machine etc or waste's from dryers, so for plug top's, I don't see that as an issue IMO.
 
Well, would you Adam & Eve it.

Went to do a quote this morning. Lady had had a kitchen installed by her builder in new extension. Apart from him ball'sing up the worktops etc, she had an integrated fridge freezer, plugged into a socket directly behind it, and free standing washing machine, built in, also with socket directly behind. Well one assumes so, 'cos you got to remove the appliances to check. :eek:
 
Another good reason for no sockets behind appliances - testing and fault finding.
Just realised that's two reasons.

Reminds me of a monty python sketch. Our two weapons are fear and surprise!
 
I have in the past, put a socket behind a built in appliance, with DP switch above (my own kitchen). I wouldn't do so now, simply because if the fuse in the plug top goes, there's a certain amount of dismantling of the kitchen unit & appliance to access said plug top. I know, because I've had to do so in my own kitchen :mad:.

I now install with DP above worktop & socket in adjacent cupboard, or as some customers prefer, just socket in adjacent cupboard.

As regards the advice from building regs, about not putting sockets on or in kitchen units, what advice do they give about under cupboard lighting, and Mrs Miggans and her socket for her mixer on her island unit :)

Ah I'm glad to see Mrs Miggans is back, you haven't done a job for her for a while. :D
 

Reply to Wiring a kitchen and where you put appliance sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
988
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
641
A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock