My old hard wired 30 amp oven blew just before Christmas. I bought a new 13 amp one. In order to get it up and running for Christmas I hard wired it into the 30amp circuit. All kitchen wiring and consumer unit were renewed just under 30 years ago.
There is a 13 amp single socket next to the cooker switch under the worktop which runs the ignition for the gas hob.
Question which is the best option;
a) Leave it as it is
b) Change the breaker in the CC to a 13 amp one, keeping the oven hard wired to the heavy duty cable back to the CC
c) Change the socket to a double and use that. It will be a tight fit as the existing socket just fits between the side of the cupboard and the switch for the oven.
d) Anything else ?
 
Replace the outlet of the old 30A with a good quality single 13A socket, and plug in the new oven. You can leave the breaker as it is.

The igniter socket may well be a spur off the ring,…. Not something I’d like to use for a heavy load appliance.
 

Reply to Wiring a New Oven after change in ampage in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
718
Good evening, I am new to the forum, and I am after some advice I am looking at buying my son a new oven, but have just noticed that the one I...
Replies
2
Views
2K
I purchased a new-build apartment 10 years ago, which came with a fitted oven and microwave. Both appliances are described by the manufacturer...
Replies
1
Views
777
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
715
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock