Any of you guys have experience or comments regarding this one ?

I am helping a friend wiring their trailer from scratch.

Fitting a 4 way IP 55 board with 30ma RCD and a 16A roundpin single phase female for there hook up supply.

I plan on wiring the sockets in 2.5 3 core arctic blue flex as radials and protected by B type 16A mcb's

And lighting in 1mm flex on a 6A

Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok.
I think the answer is yes but it never hurts to check,
Oh yes, bit late but HAPPY NEW YEAR.:angel_smile:
 
Why wire in flex? Will you be wiring from underneath? (ie. outside?). And surely you wouldn't expect them to plug in a potentially live male commando plug into a female socket?
 
Any of you guys have experience or comments regarding this one ?

I am helping a friend wiring their trailer from scratch.

Fitting a 4 way IP 55 board with 30ma RCD and a 16A roundpin single phase female for there hook up supply.

I plan on wiring the sockets in 2.5 3 core arctic blue flex as radials and protected by B type 16A mcb's

And lighting in 1mm flex on a 6A

Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok.
I think the answer is yes but it never hurts to check,
Oh yes, bit late but HAPPY NEW YEAR.:angel_smile:
flex is the cable of choice for vehicles and anything vibrating...
 
Why wire in flex? Will you be wiring from underneath? (ie. outside?). And surely you wouldn't expect them to plug in a potentially live male commando plug into a female socket?

Exactly the opposite regarding the male commando. Think about it !!

Flex for caravans and trailers due to vibration ect.

And its a mobile unit so hookup could be any 16A supply where ever they are.

Be nice guys, (Give him enough rope to hang himself) That's not a tradesman talking, but we know the type, there's always one. lol.
 
Exactly the opposite regarding the male commando. Think about it !!

Flex for caravans and trailers due to vibration ect.

And its a mobile unit so hookup could be any 16A supply where ever they are.

Be nice guys, (Give him enough rope to hang himself) That's not a tradesman talking, but we know the type, there's always one. lol.
already mentioned at #6
 
You've not mentioned an earth bond to chassis, you will need to do that

Quote" original post
Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok. Unquote"

But your comment is appreciated itselectric and a valid and useful one. Of course bonding of extraneous conductive parts, including the chassis will be completed.

Looks like my choice of cable is ok. As Glennspark as pointed out ref 6
Thanks mate.


 
Quote" original post
Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok. Unquote"

But your comment is appreciated itselectric and a valid and useful one. Of course bonding of extraneous conductive parts, including the chassis will be completed.

Looks like my choice of cable is ok. As Glennspark as pointed out ref 6
Thanks mate.



Plug and socket arrangement?
 
Quote" original post
Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok. Unquote"

But your comment is appreciated itselectric and a valid and useful one. Of course bonding of extraneous conductive parts, including the chassis will be completed.

Looks like my choice of cable is ok. As Glennspark as pointed out ref 6
Thanks mate.


your welcome Bald.:wink:
 
OK Baldy, I've decided to play nice :D

Working on mobile units can be a bit of a minefield if you're not exactly sure what you're doing. I must say that I am no 'expert' but I have worked on them before. You sound like you are planning on finding hardwired supplies from wherever you take the trailer, if this is the case then there are a few things you need to take account of, the first one being.... The fixed supply plug on your trailer needs to be male, to be able to accept a female socket on to it.

Secondly, you need to be able to make sure that the trailer is never used as part of a TN-C-S system unless directly under your supervision. This can realisticly be achieved in one of two ways; 1. relying on a rod and an RCD whenever you're plugged into a permanent supply (making your trailer a TT system), or 2. relying on electrical separation as your protective measure for if you're plugged into a generator. This method is by far the safest method of protection and I would choose this over ADS any day of the week!

The way to set this up is ultimately to wire as you normally would any installation with an RCD as your main switch, preferrably a 10mA, and making sure that all exposed conductive parts within the trailer are supplementary bonded to themselves and to the chassis (remember that this is not an extraneous conductive part). The other thing worth noting is that you will not have an earthing conductor to your fixed supply plug as you will either be relying on an earth rod or on no earth reference at all. At no point will you want to be picking up an earth from the supply unless you can be absolutely sure that every single supply you tap into is TN-S.

If wiring into a permanent supply you'll obviously have to bang a rod in (wired from your main earthing terminal) every time you park up and do business. This will have to be tested on every occasion you do so and you will go through a few rods! lol. If plugging into a genny then you will be relying on electrical separation and therefore you want nothing earthed (no rod!), only bonded to each other, which is effectively what your cpcs now become in each circuit. Bear in mind that your RCD is now useless when relying on a generator with no tapped earth. An ideal wiring system would be stranded cable to BS 7211 (I think) wired within plastic flexible conduit throughout the trailer. This is so you can get a 2.5mm cpc to every accessory to keep your ohmic readings between accessories negligable.

With regards to your supply, you really do want to be accurate about your demand. If you have a socket circuit which will only pull 2.5A then put it on a 3A MCB, if your lights will only pull 0.5A put them on a 1A MCB. The last thing you want is an installation on an unprotected 16A supply but with the potential to pull 38A (16A + 16A + 6A) if other stuff unrelated to you is plugged in.

I fear I am now rambling, my excuse is that I've had a few beers so feel free to shoot me down if I've left something out that I should have put in or put something in that I should have left out.
 
Exactly the opposite regarding the male commando. Think about it !!

Flex for caravans and trailers due to vibration ect.

And its a mobile unit so hookup could be any 16A supply where ever they are.

Be nice guys, (Give him enough rope to hang himself) That's not a tradesman talking, but we know the type, there's always one. lol.

Ah completely missed "mobile"!
 

Reply to Wiring up a mobile catering van. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I went to go and check some electrics on a friends catering van they have purchased. It's not a towable van, it's a long wheel base with...
Replies
22
Views
5K
This may be a daft question, but I have been asked to install an outside socket on a static caravan. As is the norm on a holiday park, the supply...
Replies
6
Views
3K
A
Hiya all What we have is a holiday home site type effort where there are 13 caravan type looking units of accommodation. They do not have towing...
Replies
15
Views
3K
Hi all, back again requiring some transportable building knowledge, this time round a catering/burger van and its earthing arrangment. Was asked...
Replies
3
Views
10K
E
Hi All, I've got a job to do at new caravan site. The client is paying for 3phase off of the pole that runs through the field and they have...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock