Hi,
does anyone know if wylex 60898's can replace it 3871 equivalent?
Just need to fit a 45a MCB for new shower a customer has fitted but he has 3871 board and I'm struggling to find a 45a 3871 and would rather fit a new mcb anyway.

Its the Wylex NSB type 2 MCB's. Couldn't get access to the board as its in really stupid position and requires taking kitchen units apart to access but could see it.

many thanks,
 
is this an old Wylex CU with the 3036 fuses replaced by MCBs? In which case 60898 can fit into the CU

If its a new circuit shouldn't use 3871s are they are not recognised anymore. New shower - manufacturers instructions usually say should be protected by RCD, I'm guessing the CU isn't RCD protected.
 
Don't think you can get a 45 amp wylex Mcb but you should be able to get a 40 amp old type NSB of Ebay wylex 3871 ncb | eBay But if is a new circuit t should be protected by an RCD so may be better getting a small shower unit DB or changing the board
 
Its actually RCD protected already and an existing shower circuit. He didn't realise he bought a higher rated shower and its been tripping the 32 amp MCB after being on for a little while, so I thought I'd look to see if I could find a 45a. Has anyone had any joy fitting a 60898 equivalent in one of these boards?
cheers
 
The older Wylex MCBs have a part of the MCB that cuts out to fit the bus bar. I have not tried the new wylex MCBs but i don't think they will fit , If you are just swapping the MCB over then go for the 3871 off ebay , I can't see it being a issue as you are not altering the circuit, have you checked the cable in man enough.
 
and just to muddy the water, as the shower is a fixed load you only need short circuit protection so you can fit a 50A MCB if you so desire. as long as the fibreglass monkeys don't come along and smother the cable.
 
and just to muddy the water, as the shower is a fixed load you only need short circuit protection so you can fit a 50A MCB if you so desire. as long as the fibreglass monkeys don't come along and smother the cable.

ah didn't think of that! I might have to go down that route as I'm still struggling to find a 45a and I'm not sure if a 40a will trip out too as i cant find any 3871 time curves at all. I'll get up in the loft and make sure the cable stays clear of the insulation! cheers
 

Reply to wylex 3871 and 60898 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Customer has a Wylex NS11 board with NSC cartridge fuses. They want some work doing, so now need RCD protection. The NHXB RCBO have always been a...
Replies
1
Views
903
I may well need to change all the MCB's for RCBO's in this board (see picture). Do Wylex RCBO's fit in this board? It is currently fitted with...
Replies
22
Views
8K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
Had a customer message me before I went to do a job asking if I could put a new bulb in a spotlight while I was there, so I picked up some LED...
Replies
5
Views
374

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock