hi folks, thought I’d share this...

Called out to a customer of mine yesterday, said that her shower switch had been making a smell if shower had been on for 10mins. Went there expecting to be a loose neutral like I’ve seen before.

The shower was a 9.5kw that had been installed and once I looked into the circuit it was a 45 amp rewireable fuse with only a 6mm cable! Connections were tight after all but the neutral side was very very burned on the load side.

As a temporary fix, I changed out the wire for 30 amp wire in the short term. Explained this to the customer as I put an amp meter on and ran the shower as she’d had it set. It ran to 42 amps - and the fuse wire held up! Set her shower to medium setting and ran the meter again and was only pulling 23 Amps.

So, if there was ever a reason to explain to customers why to upgrade their boards from fuse wire - this is a good story right here. Very dangerous and could have been a fire.
 
Jeez, I see the righteous police are straight onto this one eh? . “Temporary fix” means “temporary” until the job gets done properly!

The cable was re-terminated and switch replaced. The customer wants a quote for replacing the shower cable to a 10mm one and changing out the consumer unit.

This was 5pm on a Saturday afternoon. There was no need to just disconnect her shower completely when there was a work around as a “temporary” fix when I get back to replace
 
So you’d rock up to a customers house -disconnect their shower and walk away until you tell them you’re returning to replace their shower cable? If it was a modern day board - you’d not just de rate the MCB in the meantime to match the cable size as a temporary fix? Exactly
 
So you have admitted the cable is under rated for the maximum load, yet have left it in service? If you think that fuse wire will protect the cable then I suggest you look at the relevant curves for it and see how long it would take for it to operate at the maximum load?
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.
 
Very true Tel, but We can only work on what the OP tells us, which is that the cable needs changing to 10mm which mean he must of carried out the relevant calculations.
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.
screwfix open till 7.00pm.
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.

Doesn’t matter you have admitted leaving the circuit in a situation which could lead to a fire. Why you fitting a new DB? Could you not just fit a RCD next to the existing board?
 
And for the record - the quote I need to do for her is to replace her whole consumer unit or to just install a new 2 way board for the shower circuit. Along with the cable upgrade obviously
 
Id of made safe of left disconcected if there’s no RCD protection...... in this situation any how .

But that’s just my opinion I haven’t seen the situation first hand like the OP
 
Interesting one this as I'm not sure how I'd proceed.

Probably have been to tell the customer that it is unsafe and not to use until put right and that a quote would be with them as soon as possible.

I would certainly have got this in writing and signed by the customer.

Disconnecting their shower is not really in my remit and leaves me open to accusations of attempting to obtain money by menaces or some such legal nonesense.

Altering, in any other way than correcting, the circuit puts me at the front of the responsibility queue being the person having touched it last so I wouldn't be doing that.

Sometimes it's best to do nothing no matter how well meaning.
 
I think the Op has done all he can.

The customer is advised, hopefully in writing but at the end of the day it is not the ops property. It is the home owners.

As for BS3036 fuses. No way this complies once the correction factor is included.
 
Customer e mailed me back today and is going ahead with option of changing the whole consumer unit out - and replacing shower cable obviously.

And for the record - the customer was informed to leave the shower on the medium setting as part of the temporary fix last night and had explained the dangers.

Honestly - some people on these forums. Any chance to make themselves look all high and mighty at the drop of a hat.

And for the others - thanks for the feedback
 
We cannot totally idiot proof the whole world,
The customer knows the score,
And if they choose to do what they have been told NOT to ?
Then it is the customers responsibility.
A good workable compromise was reached
which resulted in the customer at least having some hot water.
it's called " Customer Service ".
 

Reply to Yesterday’s callout - a close call in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
985
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
714
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock