Discuss Ze of 0.50 ohms on a TN-C-S system in the The Welcome Forum area at ElectriciansForums.net

Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and record a Ze within what’s acceptable,still learning so these things keep me awake at night......
 
Last edited:
Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and recited a Ze within what’s acceptable,still learning so these things keep me awake at night......
If all his Zs reads are within parameters he potentially can. Let's be honest in domestic the R1 +R2 is so low the Zs is normally way under the permissible.
However I would make a note on cert DNO informed with name of person who ok'ed it.
 
They'll probably get you to take the Ze at the cutout to eliminate the possibility of any consumer's equipment (eg tails) causing the problem.
If they OK it get a reference number and quote that on the cert.
 
Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and record a Ze within what’s acceptable,still learning so these things keep me awake at night......

Regardless of what the DNO say he records the measured Ze on the certificate, and if everything else complies then no problem.
The figure of 0.35 is a guideline typical value, not a fixed maximum permissible value.
As long as the Ze of 0.50 is stable and all circuits comply for Zs then it is fine.
 
Regardless of what the DNO say he records the measured Ze on the certificate, and if everything else complies then no problem.
The figure of 0.35 is a guideline typical value, not a fixed maximum permissible value.
As long as the Ze of 0.50 is stable and all circuits comply for Zs then it is fine.
Apparently 0.35 ohms is the typical maximum.
 

Reply to Ze of 0.50 ohms on a TN-C-S system in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
918
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
768
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock