Discuss ZS at DB in the UK Electrical Forum area at ElectriciansForums.net

There should be no confusion at all on this one.

There is only one Ze at the installation, no mater domestic commercial industrial or whatever, and it is at the main incomer of supply, all the rest will be Zs Or Zdb, no matter how many boards you have, it is still not external is there? You may think, when you test at sub main DB, it seems like it is Ze, but it is Ze to that board only, but it is still in consumer installation, is there?

And don’t matter how you call the test at that particular DB, it is still the same test. Isolate that board first, and test the loop between incoming L and E, that’s all.
 
Last edited:

Reply to ZS at DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
481
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
658
For example kt63 calculates pfc/psc with Zs but it has no option to go for an L-N test. The calculation is also the same V/Zs or V/Ze. The kt63...
Replies
15
Views
1K
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock