Ze is only at the origin, the rest are Zs.

Measure/calculate the R1+R2 for each distribution circuit and add the Ze. (Zs=Ze+(R1+R2))
 
I have a ccu with a Ze of 0.09 and it's supplying another ccu which that board supplies multiple other CCUs I was wondering how I would work out my zs and ze on the other boards?

Ze only exists at the origin, e stands for external.

In an existing installation you measure Zs at each board.

If this is at the design stage then you need to use the calculated impedance of the circuit and add it to the Ze quoted for the supply.
 
Ze is only at the origin, the rest are Zs.

Measure/calculate the R1+R2 for each distribution circuit and add the Ze. (Zs=Ze+(R1+R2))
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?
 
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?

Yes it does become the Zs at the DB, but obviously that is also the Zs of the distribution circuit because they are one and the same thing.

Strictly speaking 'Zs at DB' or 'Zdb' are not correct terminology, much like 'ring main' instead of 'ring final circuit', everyone knows what is meant by it, it's commonly used, but it's not correct terminology.
 
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?
Each board would have its own Zs, sometimes referred to a Zdb. I think we're saying the same thing.
 
Yes it does become the Zs at the DB, but obviously that is also the Zs of the distribution circuit because they are one and the same thing.

Strictly speaking 'Zs at DB' or 'Zdb' are not correct terminology, much like 'ring main' instead of 'ring final circuit', everyone knows what is meant by it, it's commonly used, but it's not correct terminology.
But, 'Zs at DB1, 2, 3', whatever, is a statement...nothing wrong with the terminology, whatsoever.
 
Last edited:
But, 'Zs at DB1, 2, 3', whatever, is a statement...nothing wrong with the terminology, whatsoever.
I agree with ipf, but there will always be a Jobsworth that disagrees with this though.
 
Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointless.
You do your PEFC with all parallel paths connected at the origin not a ZE test .The Ze test determines the resistance of the earthing conductor external to the installation and confirms an earth connection to the installation hence it’s done with no parallel paths connected.
 
If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
You do your PEFC with all parallel paths connected at the origin not a ZE test .The Ze test determines the resistance of the earthing conductor external to the installation and confirms an earth connection to the installation hence it’s done with no parallel paths connected.
I'm talking about Schedule of test result - Zs at DB
 
ill just take it you don't have to do Zs at DB at origin DB, unless anyone says differently.
The test carried out at the origin DB is the Ze not Zs. This is done with parallel paths removed to confirm the continuity and loop impedance of the DNO supply.

Zs is done with parallel paths in place on distribution and final circuits to ensure the installation disconnection times can be met.
 
Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointless.

No, Ze is measured with the earthing conductor disconnected to eliminate parallel paths.
Zs is measured with everything connected, you carry out this measurement to establish the prospective fault current, so you might as well write the number down since you are measuring it anyway.
 
Would it be the case that Ze may not always be at the first dB, for example if tails have been extended via fused switch and swa? you'd take ze at the switch, disconnecting earthing conductor, then your 'sub main zs would also be your zs at db1?
 
Would it be the case that Ze may not always be at the first dB, for example if tails have been extended via fused switch and swa? you'd take ze at the switch, disconnecting earthing conductor, then your 'sub main zs would also be your zs at db1?
Take Ze at the switch fuse
 
Or if, as is so many older domestics, there is a separate incoming earth bar. It's the earth bar in loads of industrial/commercial systems but, because it's included in the supply details with the certificates' it's still a case of it being recorded as your main DB.
 
I have a ccu with a Ze of 0.09 and it's supplying another ccu which that board supplies multiple other CCUs I was wondering how I would work out my zs and ze on the other boards?
As others have said Ze is only measured at intake.
So in simple terms, if you have a Zs figure at the first DB and then install a distribution circuit to a remote DB/CU the R1+R2 value of this circuit is added to the Zs value at the first DB irrespective of the Ze as the Zs at the first DB will already include/allow for the Ze value.
Subsequent distribution circuits are then added to (if in series) or calculated separately if in parallel.
 
I have another question, so... instead of starting another thread

Zs via measurement is a live test, so if I'm testing a plug socket Zs - so once the Live current reaches the MET all Earthed and Bonded metal work will become live - seems a bit dangerous - what is the current and voltage the meter uses for the test?
 
No. The MET will be, if all connections correctly made be at earth potential (0v with respect to the live of 230v).
Test voltage 230v.
 
Zs via measurement is a live test, so if I'm testing a plug socket Zs - so once the Live current reaches the MET all Earthed and Bonded metal work will become live - seems a bit dangerous - what is the current and voltage the meter uses for the test?
If the Earth is connected to the MET reliably then you get current flowing but the increase in local potential should be negligible in the test.

But clearly if you had a situation where the local MET was not well earthed, say missing wire or badly corroded terminals, or even with an earth rod for TT that could well have an Ra of 200 Ohms and be perfectly acceptable, then there is a very real risk of the local earth/CPC arrangement becoming live w.r.t. the true Earth to a dangerous potential.

It is possible that modern MFT have some safety features included, but I don't know for sure. For example, if you were diverting your Zs test current of a few A from L to E and you observe E going to many volts above N, this is not good, and you could reduce the test current and still get a measurable Zs result.

However, what I do know is the "no trip" type of Zs test only uses a small current (probably 15mA) so it won't trip an RCD and then correlates the cycling of that on/off over a long period to see the resulting mV (or less) change in supply voltage. In this case you are not at real risk (though getting a pulsing 15mA shock won't be nice) but the test is less accurate than a high current Zs that generates a more easily measured change in voltages to deduce the impedance.
[automerge]1589706640[/automerge]
More likely a MFT would do a low-current test first, and if that caused very little change in potential difference, then up the test current.
 
Low current loop test is around 15mA to prevent RCDs from tripping. High current test for the Megger is 25A.

As live testing is in the final stages of testing the earth connections would have been proven during dead testing meaning the earth terminal voltage should not rise when testing. Also you shouldn't be touching the terminals when testing anyway.
 
Would it be the case that Ze may not always be at the first dB, for example if tails have been extended via fused switch and swa? you'd take ze at the switch, disconnecting earthing conductor, then your 'sub main zs would also be your zs at db1?

Ze is not at any DB, Ze is the earth fault loop impedance of the incoming supply.
The e stands for external, it is is the impedance external to the installation.

Ze is the earth fault loop impedance at the incoming supply terminals,
If the supplier has provided an isolator then it is measured between the outgoing L terminal of the isolator and the disconnected earthing conductor, if there is no isolator then strictly speaking it is from the outgoing L terminal of the meter. As meters are sealed we normally measure at the closest L terminal to the meter that is available
 
Ze is not at any DB, Ze is the earth fault loop impedance of the incoming supply.
The e stands for external, it is is the impedance external to the installation.

Ze is the earth fault loop impedance at the incoming supply terminals,
If the supplier has provided an isolator then it is measured between the outgoing L terminal of the isolator and the disconnected earthing conductor, if there is no isolator then strictly speaking it is from the outgoing L terminal of the meter. As meters are sealed we normally measure at the closest L terminal to the meter that is available

Yeah, I get that, so practically, often if no isolater etc is available ze will be taken from the top of the L N terminals of the main switch inside the first dB won't it? That's what I meant.
 
Thanks, Still interested in what voltage Loop Impedance testers use?

You could say you shouldn't be touching this and that but you know Zs tests take place without any preparation and probably R1+R2 is calculated from Zs tests etc.
 
Thanks, Still interested in what voltage Loop Impedance testers use?

You could say you shouldn't be touching this and that but you know Zs tests take place without any preparation and probably R1+R2 is calculated from Zs tests etc.

It is conducted at whatever voltage the tester is connected to, usually 230V nominal.
Any modern tester will monitor the voltage rise on the earth during the test and stop the test if it rises above a certain value.
 
Ok thanks, surprised if it actually uses 230v for the test and doesn't use a transformer.

but maybe people should think a bit more before just plugging there tester into a socket and letting whatever A.C voltage 15mA flow through the earth etc.
 
Ok thanks, surprised if it actually uses 230v for the test and doesn't use a transformer.

but maybe people should think a bit more before just plugging there tester into a socket and letting whatever A.C voltage 15mA flow through the earth etc.
There is no danger,If the meter detects that the voltage rise is above the meters setting, typically 50v to earth then your meter will abort the tests, so the danger is removed.
 
There is no danger,If the meter detects that the voltage rise is above the meters setting, typically 50v to earth then your meter will abort the tests, so the danger is removed.
Even a low voltage it might not be a "Danger"
but a child touching a metal faceplate in a residential property while a break in the CPC during such test it's obviously not very good, you can say you shouldn't be touching this and that but like I say some people probably don't take any precautions and work out R1+R2 from Zs test without even thinking a Live Current is flowing through the CPC.
 
Even a low voltage it might not be a "Danger"
but a child touching a metal faceplate in a residential property while a break in the CPC during such test it's obviously not very good.
The meter will not let you carry out the test if the voltage to earth rises above 50v by a break in the continuity of a cpc connecting to any exposed conductive parts
If we are talking initial verification, then continuity of the cpc and the connection to earth of any exposed conductive parts should have been verified before any live testing as prescribed in part 6 of bs7671
 
Ok thanks, surprised if it actually uses 230v for the test and doesn't use a transformer.

but maybe people should think a bit more before just plugging there tester into a socket and letting whatever A.C voltage 15mA flow through the earth etc.

How would you connect a transformer to be able to test the loop impedance of the supply at anything other than the supply voltage?
 

Reply to Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
601
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
533
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
830
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
359
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
179

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock