Discuss Zs too high at distribution boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

The easiest solution really is to fit RCD/RCBO but as we all said investigation should be in order. Im my experience if this is an older installation with all the entails it may be the original design called for a type 1 or B MCB and over the years for various reasons other types have been fitted.
 
If you let me know the distribution circuit cable details (CSA, approximate length, is the swa alone being used as the cpc) then I can calculate the R1+R2 and we can then see if there is a fault.

The R1+R2 added to your Ze of 0.08 Ohms will give us a worst case scenario, with actual parallel paths, your measured Zs should be lower than my calculated figure.
 
If you let me know the distribution circuit cable details (CSA, approximate length, is the swa alone being used as the cpc) then I can calculate the R1+R2 and we can then see if there is a fault.

The R1+R2 added to your Ze of 0.08 Ohms will give us a worst case scenario, with actual parallel paths, your measured Zs should be lower than my calculated figure.


:) good post.
 

Reply to Zs too high at distribution boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
548
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock