K

knasher

The boards i tested were none RCD protected, with 60A sub main protective device. Is the easiest way to solve the problem to install a main RCD incomer, eg 63A, 30mA at each DB? any advise?
 
Check Ze at origin, if that is OK then you need to find problem further downstream. If its not OK and no obvious problem contact supplier.

Cheers...........Howard
 
What figures for Zs were you getting at the boards?


Sent from my iPhone using Tapatalk.
 
sorry just picked up all other responses to my query. Ze at origin is 0.08,(should be 0.35 shouldnt it for TN-C-S? Also, yes it was a PIR that picked up these issues. Also, re. your response (splindon), Yes, point taken re.sec.314.
Have read PIR further and looks like earthing conductor is too small 10mmcsa instead of 16mm. Supply conductors are 35mm. Could that be the likely cause?
 
think you.ve answered your own question .10mmm way too small . Ze should be max. 0.35. anything under is good.
 
Zs figures at DB's were 0.37, 1.13, 0.12, 0.95,0.13. overcurrent protective devices were 3871 mcb, 60A. some Zs figures seem acceptable, but not all (GN3 used)
 
a 10mm earthing conductor instead of 16mm IMO wont cause a dramatic increase in ZS. when designing jobs, i would use the max Ze to workfrom, as its worst case scenario. it could be something simple like corrosion on the armour, or no link from the glandplate/banjos to the earthing bar in DB
 
thanks for all your input guys, this site is a great help to someone who is not ashamed to admit that I have only recently got my City & Guilds (In response to Tonys question, "am I an electrician?", no I feel as though I've still got a lifetimes learning ahead of me still, but find this whole subject fascinating. Cheers
 
Yes, you would never get 0.08 Ohms by enquiry.

The earthing conductor size is not an issue as regards Ze/Zs.

What is the type of the BS 3871 devices?
 
So you have 2 DB's with exceeded maximum Zs values.

Are these DB's much more remote or supplied by smaller CSA distribution circuits?

I'm really asking if this is down to poor design or cpc continuity faults on the distribution circuits in question...
 
Hi Knasher
Max Zs for 63amp 3871 mcb is 0.76 Ohms. with your Ze at 0.08 even if you uprated your main earth conductor too 16mm it wont make a differance to the high readings you have on some of the Diss board's. Check the connections off the Glands if it is on SWA's, corrosion on the armouring will draw the readings down. Use a P-Nut lock nut with a suitible supplementary to the earth bar on both ends will help.
 
It's a BS 3871 type 2 60A !

I make it a maximum of 0.55 Ohms tabulated, 0.44 Ohms at 80% value????

It's so important to get these figures right as the o.p. could (rightly or wrongly) use them in his diagnosis!
 
Found a bit more info from PIR guys and it includes: absence of supplementary bonding in places (been given code 1, which seems a bit bit extreme - wouldn't it be code 2?). Also, mentions poor connections on some ring final circuit patresses in certain offices. Another point mentioned is main bonding being terminated at sub distribution boards and not MET. All of these things could affect Zs couldn't they? Excuse my ignorance.

One final question for IQ electrical, can you tell me how you got your Zs figures - i've looked in GN3, OS guide and BS7671, applied rule of thumb etc but am none the wiser. Can you enlighten me. Cheers again everyone!
 
Yes, the type 2 trips at up to 7 times it's rated In current so from Ohms law, you get 230/420

That's 0.55 Ohms, 80% value of 0.44 Ohms
 
Found a bit more info from PIR guys and it includes: absence of supplementary bonding in places (been given code 1, which seems a bit bit extreme - wouldn't it be code 2?). Also, mentions poor connections on some ring final circuit patresses in certain offices. Another point mentioned is main bonding being terminated at sub distribution boards and not MET. All of these things could affect Zs couldn't they? Excuse my ignorance.

One final question for IQ electrical, can you tell me how you got your Zs figures - i've looked in GN3, OS guide and BS7671, applied rule of thumb etc but am none the wiser. Can you enlighten me. Cheers again everyone!

Code 1 for absence of supplementary bonding?
What were the locations lacking supplementary?

Connections to back boxes are imperative with conduit/trunking being used as the sole cpc-is this the case?
That would be a code 2 on my report.

All of those points can have an effect on Zs however in my experience , it's most likely down to the length of the distribution circuit or undersized cpc in the distribution circuit.
 
might be clutching at straws here, but, occasionally, you might fing a high resistance between the earth bar and the metal box in which it is mounted. if there is no fly lead between them.
 
Last edited:
It dont say in PIR where supplementary bonding is lacking - and its a pretty big building to explore, but still can do. As re. checking connections at back boxes, again thats easy enough. As re. length of circuit too long or under sized cpc, whats the most simple solution? install bigger cpc do you reckon?
Finally, thanks for shedding light on how you got Zs values for 3871 type fuses - didnt have a clue thats how you got figures! Cheers malcolmsamford too (havent checked out link yet but will do).
Is there any logical sequence to approaching problems like this or is it down to years of experience?
 
The easiest solution really is to fit RCD/RCBO but as we all said investigation should be in order. Im my experience if this is an older installation with all the entails it may be the original design called for a type 1 or B MCB and over the years for various reasons other types have been fitted.
 
If you let me know the distribution circuit cable details (CSA, approximate length, is the swa alone being used as the cpc) then I can calculate the R1+R2 and we can then see if there is a fault.

The R1+R2 added to your Ze of 0.08 Ohms will give us a worst case scenario, with actual parallel paths, your measured Zs should be lower than my calculated figure.
 
If you let me know the distribution circuit cable details (CSA, approximate length, is the swa alone being used as the cpc) then I can calculate the R1+R2 and we can then see if there is a fault.

The R1+R2 added to your Ze of 0.08 Ohms will give us a worst case scenario, with actual parallel paths, your measured Zs should be lower than my calculated figure.


:) good post.
 

Reply to Zs too high at distribution boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
509
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
565
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top