    HELP...Kitchen wiring inadequacies??.

    Thanks for your reply Midwest. I appreciate that no one suggested keeping the 2.5mm cable to the island to run the hob and socket but at the same time whilst advising me it was viable with diversity I was expecting some responses being alarmed like myself that they wanted me to install a cable...
  2. C

    HELP...Kitchen wiring inadequacies??.

    Thanks for the reply's again all very much appreciated. I appreciate what you have said about the 2.5mm cable to the hob and 13A socket for the island but even with that diversity applied it would still be around the max carrying capacity and my mrs will have all 4 plates of that hob at full...
  3. C

    HELP...Kitchen wiring inadequacies??.

    Thanks again. Good idea with the 45A connection points then a back box for either connecting a socket face or an fcu but another slight problem is that there is nowhere to put any switched items as the cupboards are boxed in floor to ceiling so only option would be to place inside the top...
  4. C

    HELP...Kitchen wiring inadequacies??.

    Thanks again chaps much appreciated but I think you will find that the whole purpose of this post was because I disagreed with the drawings that were sent to me and wanted to confirm this so I could wire this as per most of the advice so the general confirmation is what I was after although if...
  5. C

    HELP...Kitchen wiring inadequacies??.

    Many thanks for the reply's to date. Up until a couple of years ago one of the companies I work for were NICEIC registered and obviously part P was automatic when a fully registered member but we let this go when we wound that side of the company down. I will be going through local building...
  6. C

    HELP...Kitchen wiring inadequacies??.

    Sorry guys I'm sure these points have been raised before but been busy searching. I have been sent a diagram by the shop where we purchased our kitchen for the electrical wiring requirements and positions. I am a electrician to the 17th edition by trade but it's not my every day job nowadays so...
  7. image.jpeg

    image.jpeg

  8. image.jpeg

    image.jpeg

  9. image.jpeg

    image.jpeg

  10. C

    Preferred Bathroom Power Supplies?

    Thanks guys much appreciated and yes it is abit overkill (pardon the pun) but it is for family. just a quick point sorry for the confusion but it was a mirror demister pad I was talking about although there will be UFH as well. oh and for the few critics out there, yes as a sparky I probably...
  11. C

    Preferred Bathroom Power Supplies?

    Both on RCBO's
  12. C

    Preferred Bathroom Power Supplies?

    Hi Guys Was just wondering what you thoughts are on the following; En-suite Bathroom - Require power for ceiling in line fan, Power for towel Rail heater, Power for Shaver Socket, Power for heated mirror mat, Power for light above mirror, Power for light in wall cuboard. There is obviously...
  13. C

    Help Needed!!

    Yep sorry about that, Risteard is right. Although your calculations are correct the regs (including the on-site guide) state you should assume a min of 100w at each point. Should have remembered they always try to catch you with that one. Long time ago.
  14. C

    Help Needed!!

    Hi Sparky, You dont need any help, what you have done is correct. We used to say 1KW (1000 watts) was 4amp just for ease but on actual figues using 230v you are spot on. Obviously a standard 1.5mm square twin and earth will carry considerably more amps than that so could in theory be fused at...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock