Discuss Help Needed!! in the Australia area at ElectriciansForums.net

S

Sparky_2607

Hi there, first post so be gentle!

Now i have had some work set by my college and I just needed your help to check wht i have done is right. So the question is:

How many lights (60 and 100W) can you run off a 6 amp MCB in a domestic home?

Now I have worked it out to be,

230*6 = 1380

1380/60 = 23

1380/100 = 13.8

so

60W is 23 lights in a domestic home

100W is 13 lights in a domestic home


So i ask you, is this correct and if not, could you direct me as to where i have gone wrong?

Many Thanks (sorry its long winded)
 
Hi Sparky,

You dont need any help, what you have done is correct. We used to say 1KW (1000 watts) was 4amp just for ease but on actual figues using 230v you are spot on. Obviously a standard 1.5mm square twin and earth will carry considerably more amps than that so could in theory be fused at a higher rating if more load was required depending on exactly what type of lighting was involved etc.
 
You should assume 100W at each point (not 60W).

Although, with application of diversity you could increase what you are supplying from a 6A circuit breaker.
 
Last edited:
Yep sorry about that, Risteard is right. Although your calculations are correct the regs (including the on-site guide) state you should assume a min of 100w at each point. Should have remembered they always try to catch you with that one. Long time ago.
 
Sparky 2607, i agree with your calcs, but just to keep you on your toes I will throw one back to you. Which 6a MCB would you use in that installation and why?, Type B,C or D.

Cheers..........Howard
 
Last edited by a moderator:

Reply to Help Needed!! in the Australia area at ElectriciansForums.net

Similar Threads

https://www.walmart.com/ip/Minecraft-Green-Creeper-Body-12-Can-Mini-Fridge-8L-2-Door-Ambient-Lighting-25-2-H-9-5-W-9-1-D/2670909566 ok so let me...
Replies
3
Views
537
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
I am a retired Electrician and started looking at Solar Power, (Black Magic to me), after much reading of "How To", I decided to build myself a...
Replies
10
Views
1K
Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
510
Hi, sorry if this has already been discussed or is in the wrong place. Im wondering if anyone has come across a domestic EV charger where the ct...
Replies
1
Views
579

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock