Hi,
Normally we use Garo units as PEN fault detection units, however, this is a 3 phase installation so a rod is much cheaper in this scenario. Agree with the cost difference in cable, I will go with 5 core SWA. It wasnt so much the money, it was more about the efficancy of the installation not...
Hi,
Thanks for the advice appreciated, think I will run it in 5 core swa and run the earth back to the board keeping it separate from the pme earthing system.
Hi all,
Hope you are all well and all is good.
I'm having to install an EV charger tomorrow on a 3 phase TN C S earthing system, however, I need to TT just the charger and am going to put in a spike and run the earth only to charger keeping separate from the main supply fuse board. My question...
Hi all,
Bit of a dilemma, hoping someone can help.
Im running a supply to a garden out building, from a 40 amp RCD protected type b mcb at the main board. The first 8 meters or so are in twin and earth and will be in plastic conduit, the second lot of cable is swa, clipped direct to an outside...
Hi all,
Hope you are all well and all is good!
Can anyone recommend a nice looking garden light that can be surface mounted with side or bottom entry, e.g. can be retro fitted with surface mounted cabling?
Thanks in advance,
Martin
Hi all,
Hope you are all well and all is good!
I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding a 25mm 3 core SWA at a length of about 2 meters to the main DB (both boards are metal). I am being challenged in saying that I have to add an earth...
Hi all,
Hope you are all well and all is good.
Was just wondering which tails you guys use to go from a Henley block to a Garo / Matt-e EV unit. I'm fed up of fighting with them, are there any super flexible ones and what size do you tend to use?
Also which cable glands do you find the...
Hi all,
I have been asked to fit an extractor fan to a bungalow, normally I chase out a box for the fan isolator and locate it above the bathroom door, is there a reason I cant locate it in the loft, im guessing due to accessibility or something, but just wanted to check?
Many thanks,
Martin
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.