Hi all,

Hope you are all well and all is good!

I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding a 25mm 3 core SWA at a length of about 2 meters to the main DB (both boards are metal). I am being challenged in saying that I have to add an earth fly lead at both ends, preferably the same size as the CPC e.g. 25mm, as the glands will be fine for continuity of CPC into the armour.

Am I being super safe or just a moron, whats the right answer?

Thanks all.
 
i would add fly leads to ensure that the steel armour is reliably earthed. seen a couple of sites where the continuity from earth bar to metal casing is poor. if you do the adiabatic, bearing in mind the restivity of the armour, 10mm should suffice.
 
Are you really competent to carry out this work, if so you would be looking at what your earthing arrangement is to the existing installation.
 
i would add fly leads to ensure that the steel armour is reliably earthed. seen a couple of sites where the continuity from earth bar to metal casing is poor. if you do the adiabatic, bearing in mind the restivity of the armour, 10mm should suffice.
Thanks Telectric, my thoughts exactly, but was just going to be over kill with the fly lead.
 
Because you are in the DIY section and messing with the DNO switch fuse? and digging around inside the existing CU therefore dangerous and maybe notifiable?
 
Are you talking about leads from the glands' banjo (or better still Earthing nut / Piranha nut) to the related earth terminals?

Yes, you should do it as you can't always be sure the box will be in great contact, not corrode a bit with time, or even (probably not here) be able to cope with the fault currents.

  • Simple answer is to go with the CSA from Table 54.7 in the regs, which in your case is 16mm.
  • Or you can go with the adiabatic calculation, and the fastest way to check that would be Table B4 from the OSG which should no change in Zs 0f 0.4 ohms from from 10mm to 16mm, implying 10mm is fully OK for a 80A fuse and 5s disconnection times.
  • Also you also really should consider the limits of Table 54.8 for the TN-C-S case in case there is extraneous stuff bonded to the CU earths, which typically means a 10mm minimum.

TL;DR Use 10mm or 16mm as you have lying around in this case!
 
Just looked over again and realised you have a CPC in the 3 cores of the SWA, that takes away the issue of TN-C-S bonding as you already have the sizeable end-end path.

However, you should still be designing to cope with an internal cable fault/penetration incident even if very unlikely, and so you should have the armour ends rated for fault-clearing of the 80A fuse.

You could get away with just 10mm at the only feed end, but I would say it is still good practice to have both ends able to cope with any fault currents. In reality 6mm at both ends should be sufficient, but 10mm would be meeting all requirements without assumptions of current sharing, etc.
 

Reply to Earth fly lead size & requirement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
890
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
294
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hi all. Could I ask some advice please regarding SWA banjo fly lead sizing. Can anyone explain what sizing or how you size the required earth...
Replies
6
Views
3K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock