t&e

  1. leep82

    C.P.C in T&E as a live conductor

    I know the thread title sounds bad but hear me out. I have wired an intermediate switch set up with feed at one switch, switch wire at another and twin and earth as my strappers between to an intermediate switch. My customer wishes to use lightwave switches for the three posistions mentioned...
  2. GBDamo

    Looped Supplys...Black flat T&E..............

    Been asked to advise on a rewire. I think on age alone it's advisable but the following points add to the argument. Installation age approx 60 years. This is a "forever Home" so although it may test ok how long will it stay so? Black T&E throughout. Not a reason to condemn alone but adds to...
  3. HappyHippyDad

    Tails (or rather T&E) behind skirting.

    Hello all. About to do a CU change and from the pre works visit it looks like the 16mm T&E from the meter is run 3m to the CU behind the skirting board. No mechanical protection seen. TNS. Ze = 0.28ohms. This clearly isn't acceptable and I shall advise getting it changed but my question is...
  4. M

    32A MCB feeding 1.5mm & 2.5mm T&E cables via 30A terminal block

    Quickie - Would you say this is ok? 32A MCB feeding 6mm T&E which is then connected to a 2.5mm T&E & 1.5mm T&E cable via a 30A terminal block in plastic terminal block housing buried in stud wall. The 2.5mm feeds a 3kW immersion heater with 13A SFU at the heater end. The 1.5mm feeds gas boiler...
  5. J

    10mm t&e submain cpc

    I know there’s the adiabatic equation to work earth size but generally if you install a twin and earth cable for distribution, do you need to worry about the smaller cpc size My situation is 20 metre 10mm t and e run and not using it to provide earth bonding. Will the 4mm cpc be adequate. 50A...
  6. Leesparkykent

    1mm or 1.5mm T&E for standard lighting circuit in your average house.

    Out of interest what's most commonly used?
  7. GBDamo

    1.5 mm T&E on a B32 MCB

    Not working on this circuit but not sure what to do. The circuit appears to only supply an unused FCU which I'd like to disconnect in the CU but as it has nothing to do with the work I'm doing I cannot spend too much time investigating the full circuit. I have isolated the MCB overnight and...
  8. M

    Bellwire alongside T&E in conduit

    I have some 20mm conduit going to the lights in my garage. I've wired them up using 1.5mm T&E in the conduit rather than conduit cable. I'm looking at routing my garage door opener cable in the same conduit, however from what I understand you cant mix low voltage cables with mains. As the...
  9. H

    16mm T&E to Consumer Unit

    Afternoon everyone, I've just been to a neighbours house who has just her home completely done up as the foundations are shot. The house has been rewired and in doing so the consumer unit has been moved to one side of the house (the main fuse is outside on the other side of house). I've gone to...
  10. yellowvanman

    1mm T&E on a 16A MCB - doesn't look or feel right!

    Doing an EICR, one circuit described as Central Heating with 1 mm T&E cable connected but on a 16A MCB. When I look closer it appears an Immersion heater has been tagged onto the circuit! I've not been able to ascertain the cable route and its installation method. This is a single storey...
  11. T

    10.8Kw shower on 6mm² T&E

    I noticed today when wiring up switch for shower the supply is in 6mm². The load cable is 10mm². The shower rating is 10.8Kw. So we have a load that is 47a on 6mm² the OCPD being 40a 60898 type B. Interestingly on the new installation (rewire) they had recently the particular cct. on the...
  12. cliffed

    10mm t&e lsoh cable

    Is there anything on the market that will ease the connection of this ridiculous cable & size. At the moment us nutties are struggling to connect into a 45 amp cooker switch,fixed on a fast fix 2g box,then struggling with a cable outlet connection,are we mad or what. Something is gonna bust,madness.
  13. 7029 dave

    16mm T&E

    I had a job last week to provide 6 meter connections . New builds and noticed in the meter box, Electricians had run in 16mm t&e from CU to external box with 80amp switch fuse. Thoughts please.
  14. Pat H

    Plastic compression glands for T&E into metal CU

    I'm sure this will have come up but what are the thoughts on cable entry into metal CUs? Obviously from the rear is simplest but if cables have to come in from below then do we need to use metal glands or are plastic ok? I assume for RFC its best for both legs of the circuit to enter together...
  15. dnjr

    2 single ovens on 6mm T&E 30A rewireable fuse

    Dear all Looked a job today in a kitchen Existing 6mm t&e supply on a 30a Wylex 3036 Lady of the house wants to change existing oven and put in 2 single ovens in one housing What's the best method of feeding these off the 6mm Can't do a double socket as it's only rated at 13 / 20 amps Was...
  16. bigspark17

    Submain 16mm t&e cpc chopped

    EICR.. 80 switch fuse in meter cupbord, 16mm t&e to cu with 6mm cpc chopped both ends and 16mm earth ran along side submain. zdb/pefc/pscc fine. bonding from db fine. i would never do this but struggling to find a reg number aggainst it :/ opinions appreachiated
  17. G

    CCP of 6mm t&e in trunking.

    Hi all how can I work out the current carrying capacity of a 6mm t&e in surface metallic trunking. I can only find clipped direct and enclosed in insulated wall using table guides
  18. D

    Plug top on 1.5 t&e

    So was sent to move some sockets today on a big office display anyway I spotted all the display light strips on extension leads made up of a 13amp plug top some had lower fuses others didn't but the plug top where on 1.5 t&e so I've now been asked to do a report on this and other bits so before...
  19. D

    6mm T&E joined to x2 2.5mm swa

    Hi, Hope you are all having a good Easter Bank holiday. Saw this the other day and just wanted people's opinions/thoughts please. (I was there installing led floodlights to the front and rear gardens only). 6mm T&E coming from the C/U into and along the attached garage wall approx 8m run...
  20. HappyHippyDad

    SWA, T&E or tails??

    Evening all.. I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock