I think you need to elaborate as how you have achieved this reading and the purpose of the test
Purpose is curiosity of my own electrical installation, and why i would have almost a dead short on N-E but with no RCD tripping unless it was a load

My flat has a circuit in it that tests as follows when live cpc and neutral are disconnected from the CU @ 250 volts

ZS 0.45

L-E >200 megohm
L-N >200 megohm
E-N 0.006 megohm
 
If it’s just the circuit you’re testing, N-E should be clear. Any load, even a neon light, would be between L-N

What is on this circuit?
Is everything unplugged if it’s sockets?
Is the polarity correct at each point on the circuit?
What are the readings at other points on the circuit?
 
If it's a radial circuit e.g. cooker/shower/maybe immersion then have you tried turning the isolator off near the load?
I'm having a stab in the dark that this is a heating element.
 
I have seen this with an old RCD socket - it had something like 50k to E as a means to trip out in the event that neutral is open or swapped.

But it could be some faulty cable of course, which is more worrying. You need to see if any loads were still connected during the test as there was only SP isolation on them.
 
60KΩ isn't going to be a design load for an appliance, do the maths and that's an Ib of 3.8mA which is daft. It could though be a Neon?
 
60KΩ isn't going to be a design load for an appliance, do the maths and that's an Ib of 3.8mA which is daft. It could though be a Neon?
agreed, I was wondering if it was a element deteriorating N to E as 3.8ma leakage seemed plausible.
I should be patient and wait and see what the circuit is!
 
Whenever I come across a reading like this, almost but not quite a dead short on the megger it usually turns out to be a surge protection extension lead plugged in somehwere.
 

Reply to 0.06 meg Ohm could it be a load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
686
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
764
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock