Discuss 0.5A difference between 2 identical inputs. Solarriver 4000TL-D in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

pdixon

-
Reaction score
2
I just had a 4kW system installed.
It uses the Samil Solarriver 4000TL-D inverter which has 2 DC inputs. There are 2 strings of 8 panels, each going to one input of the inverter.
All the panels have the same aspect and zero shading in the afternoon so I'd expect them to supply the same power at all times, more or less.

What I've noticed is that string 1 almost always has 0.5A (about 130W) higher output than string 2. It varies slightly, but 90% of the time it's 0.5A difference.

Is this normal? It looks like a big difference between what should be 2 identical strings.

At the moment, it's bright but cloudy and I get PV1= 240.9V 1.6A 397W PV2= 240.9V 1.1A 273W

The voltages happen to be identical in that reading but they do usually vary with either PV1 or PV2 being higher .. but most of the time, PV2 being 0.5A lower.

It's really odd. Even at twilight, when PV1 falls to 0.5A, PV2 drops to zero but clearly there's plenty of light out there to produce something.
I could understand it being 10% lower but not 0.5A lower.


Anyone have any ideas what's going on?
I would try swapping the 2 strings over to see if it's a panel problem pr an inverter input problem but that'll require me opening the inverter and breaking the guarantee.


Thanks,

Paul.
 
Why cant you disconnect both DC strings before the inverter and swap-over for that test - i assume they are all wired together using connectors of some description ??
 
Danesol,
I assumed the 2 strings would be plugged in to the inverter but they appear to go through grommets. I expect, without having looked, that they're wired in to some terminal block inside.
The cables appear through the roof and run continuously, through isolation switches, into the inverter. There are no connectors, at least not inside the building.

Paul.
 
Last edited:
All the panels have the same aspect and zero shading in the afternoon so I'd expect them to supply the same power at all times, more or less.

Does that mean one or both of the strings have shading at some point in the day?

I just had a 4kW system installed.

Speak to the installer. Something doesn't sound quite right and if the scaffold is still up it'll make everyone's life a lot easier to check it now than to fault-find later.
 
Speak to the installer. Something doesn't sound quite right and if the scaffold is still up it'll make everyone's life a lot easier to check it now than to fault-find later.

If the scaffold is still up, maybe that's casting a shadow on a panel or panels? Or a splodge of bird muck?

Do you know how the strings are arranged? Top row and bottom row? Left half and right half?

Or could it be that they've installed 250w panels on one string and 235w panels on the other (or similar mix-up)? Or maybe just one weaker panel on the second string may bring down the output from the whole string? It could easily be a genuine error either on the part of installer or his supplier. Not easy to check though without physically going on the roof & looking at the ID plates on the back of the panels!

Best plan is obviously to get the installer to return and explain your concerns...
 
FB,
up to 11am there is shading as the panels are on the other side of the roof.
Around 10:30 the array starts to move out of the shade but it takes until 11:00 for a shadow from the chimey to completey move off. The whole array is then in sunlight and stays that way until 7pm. From 11am to 7pm there is no shade at all.

The Panels were installed on Wednesday, the scaffolding went down on Thursday. You'd think they'd have left it up for a few days, just in case of problems!

I have e-mailed the installer. He was planning on coming on Monday anyway to check things over but I wanted to see if anyone else had any experience of this sort of thing.

It has occurred to me that maybe the inverter is just reporting bad figures. How accurate are the inverter's own measurements?

The fact is, if there had been only 1 input on the inverter with all the panels connected to it then I probably wouldn't have though there was any problem. But because there are 2 to compare and one is different it attracts the attention.

Paul.
 
Whinmoor,
no scaffolding left, but I did think that was the problem the first day before they took it down.
No sign of bird droppings, but would that cause a 0.5A drop at all light levels? Surely it would cause more loss at higher output? That's what I don't understand.

There are 16 panels in 2 rows of 8 with the left 8 being string2 and the right 8 string1.
I saw the panels when they put them up, they all looked identical to me.
Mixing 235 and 250 would cause the same percentage drop in output. Not 120W drop at all light levels, wouldn't it?

Paul.
 
I would imagine that it is the inverter giving dodgy readings. I can't seen any other reason for it.

When the installer returns to carry out his tests, I imagine he will find that current reading the same on both strings.
 
Agreed.
Maybe best to inform the installer in advance and he might be able to bring a replacement inverter with him which could save him coming back again.
 
The installer couldn't account for it and says he'll ask the manufacturer.

I was wrong about the connections from the strings to the inverter, they are plugs, but need a couple of screwdrivers to release them. I swapped the strings over and the inverter readings don't swap so it's an inverter problem, not a panel problem.

The sun came out and the inverter reported a peak of 18.3A grid current on a single phase and 4550W output from a 4kW array. I've got a feeling the inverter is mis-reporting measurements but I've been asked to keep an eye on it and take some screen shots to send to the manufacturer if it happens again.
 
erm, what readings are we actually talking about here? DC input I assume, in which case presumably the installer has verified the measurements with his own meters?

If so then it looks to me like you've either got a panel that's dirty / shaded a little, or a slightly duff panel that's pulling the ampage of that string down.

Alternatively if the installer measured the readings and they don't tally, then yes it could be the inverter giving dodgy readings.

My hunch would be that it could be you've got panels with quite variable voltage / ampage characteristics from one panel to the next, and with both strings run in parallel it's operating at the peak voltage point for one string, but not the other. Buit it's really all educated guesswork doign this remotely.
 
I have exactly the same problem with the same inverter on a set of 6+6 SunPower panels. PV2 is on average 25% down on PV1 regardless of which string is connected. This would leave me down by 12.5% of the power I should be generating. My installer has escalated this to Samil who are investigating.
 
In my opinion, Samil is a cheap terrible inverter. 2nd inputs are generally weaker than the first inputs, I'm guessing thats why most inverter manufacturers tell us to put more panels on DC 1 input over DC 2 input. A consistent 0.5a is a huge amount over a year, if it has been pinpointed to the inverter, get it changed asap. If not, ask to see the panel test doc when they installed your system, see if that shows any variations.

Also, 18.3 grid current? Am I right to assume they got DNO permission before installing as that installation wouldn't fall under G83...
 
I've been waiting for some suitable weather to do some tests.
I need some full on sun in mid-afternoon to get the output up to 4kW again but we haven't had that sort of weather since I first started this thread in September.
I'll then compare what the inverter says to what the generation meter says.

I suspect that the inverter is mis-reporting what's going on.
If that's the case then I'm not too bothered by it.

Let's hope for some good weather soon. Today was my best production day since I got the panels in with 24kWh but it only peaked at 3.6kW.
 
24kWh a day is pretty good, the sort of number you'd want to see on a standard 4kWp system. Was 3.6kW before inverter or after? (DC or AC side)
 
OK, the man at Samil is still pondering my request for a new inverter and is sending the data I have provided to China for evaluation.
Meanwhile, a pallet arrived today with a new inverter on it! My PV installer has either bitten the bullet and sent one or they have advised Samil of the error of their ways. Either way, it's being fitted tomorrow AM. We'll see if it's any better.

Incidentally, Samil's data sheet for the SolarRiver claims an MPPT efficiency of 99.90%. With a 0.5A or in my case 25% shortfall on one MPPT, this cannot be the case and would therefore come under the "Not as described" section of the Sale of Goods Act 1979 (as amended)?
 
99.9% MPPT efficiency doesn't relate to the displayed differences between each MPP tracker's values on the LCD. It's related to the ability of the maximum power point tracker's algorithm to actually achieve the "maximum power point"....it's a bit of a useless metric tbh
 
Thanks for this. Maybe my understanding of MPPT is flawed.
With 2 strings of 6 panels, both with the same orientation (-5 degrees off South) and no shadow, should they not be producing the same power IF the MPPT's are working correctly at 99.9% efficiency?
The strings have been swapped to prove the panels are not at fault
Could it be just a display fault?
 
I've done some tests with mine and I'm sure it's just the inverter displaying the wrong values.
It's been cloudless today so when the output was leveling out at its peak in mid afternoon I took 3 measurements.
1 Just string 1.
2 Just string 2.
3 both strings.

When I measured output at the generation meter (which I assume is properly calibrated) then String 1 gave 1756W (inverter read 1885W!), string 2 gave 1726W (inverter read 1728W) and together they gave 3420W.
So it looks like the inverter is reading high for string 1 but really both strings are giving out about the same power.
 
I have an indentical issue. A Samil Solar River 4000TL-D connected to 2x8 panel strings. PV1 always shows higher power output in all conditions by around 5%. installer diagnosed panels are OK by swapping inputs to inverter. New inverter arrived today so will see if there is a difference.
 
Was there a solution to this problem?
I'm on my 2nd Solar River 4000TL-D, both are reading consistantly low on PV2.
2 identical 2kw strings, due south facing - PV2 reads low even if strings are swapped round.
Low light (early morning and late evening) see PV2 reading around 45-50% lower than PV1, peak light sees around 10% lower.
Anyone got an answer?
 
Because this inverter is with 1 solar tracker their always will be difference between two strings. This is not really the ideal type of inverter.
The stronger string always will inject energy to weaker string.
You can use a string diodes to block this energy flow. I such cases better all panels to be in one string. (if it is OK with voltage at open circuit) .
High voltage - less current - less power loss, the other thing to be designed in that way.
 
Glad i found this thread, i noticed the exact same issue too.

4kW pv installed yesterday and i noticed string 2 performing around 0.5a less. The actual generation exceeded similar installs in the local area so i don't think there is any particularly wrong.

Have you concluded this is just an optimistic reading on string 1 or do we think the 2nd string is not a strong? Because it is cheap chinese kit? :)
 
A replacement Samil Solar River 4000TL-D was provided by Samil with firmware version 1.90 and the installer fitted it. The apparent difference between PV1 and PV2 output was still evident even when string swapped round so original inverter was refitted. Samil say they have a similar problem in Taunton and would get back to me. Have they?? No.
 
I'm on my 3rd inverter now and finally have one that is as close to working as I think I'm likely to get.

PV2 trails PV1 very slightly, but no where near as pronounced as the first two inverters.

This one is firmware V1.80 - the last one was V1.74, and the first one was V1.70.

Interestingly enough, the only firmware available of Samil's website is V1.70

I think it is string PV2 reading low, as opposed to PV1 reading high - simply because of startup and shutdown times. On my install, PV1 would "start" a good 45 minutes before PV2 and still be generating a good half an hour after PV2 had switched off..

This is my first day with inverter #3 so I'll post an update after a sunny day...
 
Update - after 2 visits each with a new version of the firmware Samil emailed me with a firmware upgrade which seems ot work. The 2 strings are now showing within a few watts under identical conditions. Apparently the issue was with the way the 2 strings were tracked.
 

Reply to 0.5A difference between 2 identical inputs. Solarriver 4000TL-D in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi i have a 4kw samil power solar river inverter. when i log on it reading for pv1 shows zero for pv 2 i checked both strings with multimeter and...
Replies
3
Views
4K
F
A few weeks ago, I had my solar panels remove from my roof and then replaced. Sadly, on removal, one panel was warped and on letting the fixing...
Replies
1
Views
2K
R
Five days without solar but guess I haven’t missed too much yet, thanks to the grotty weather. I’ve had my solar installation since June 2011...
Replies
29
Views
4K
iconnect
I
G
Hi all I have just had a 3920KW Sharp 16 X 245W panels fitted with a Solar River SR4K4TLA1 inverter. There are 2 strings. One is currently...
Replies
30
Views
7K
garty611
G
L
I had 3.96Kw system installed along with a mastervolt K5500 inverter last November. We had various issues with performance and the system...
Replies
23
Views
4K
lennyg
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock