I was re-testing a brand new install for QC purposes todayand the N-E on the IR was 0 Megohms, am I right in expected the RCD to trip. Itwas a TN-C-S system so wondered if the shared neutral and earth may have aneffect?
The IR for L-N and L-E belled out perfectly, I haddisconnected both the neutral and earth from the board to avoid anyinterference. There was nothing plugged in or spurred, but I wouldn’t expectthat to matter anyway on N-E. The only thing I didn’t do was put a load on thecircuit – would this make any difference?
Can anyone shed any light?!?! Thanks, Andy.
 
The RCD will only trip if there's a load on the circuit. Even with an IR of 0 Megohms N-E there will be no actual leakage current if there's no load on the circuit.
 
You say 0 megs but did you try to read ohms? If so what was it, minus the leads?
Were you testing from the db or in the field?
Sounds like you took the wrong neutrals out the db though.
 
Hi All

I was re-testing a brand new install for QC purposes todayand the N-E on the IR was 0 Megohms, am I right in expected the RCD to trip. Itwas a TN-C-S system so wondered if the shared neutral and earth may have aneffect?
The IR for L-N and L-E belled out perfectly, I haddisconnected both the neutral and earth from the board to avoid anyinterference. There was nothing plugged in or spurred, but I wouldn’t expectthat to matter anyway on N-E. The only thing I didn’t do was put a load on thecircuit – would this make any difference?
Can anyone shed any light?!?! Thanks, Andy.

Hum, probably only you when you report back on your follow up investigation!

I'd start by pluuging something into the socket concerned and see what happens next!
 
Hi All

I was re-testing a brand new install for QC purposes todayand the N-E on the IR was 0 Megohms, am I right in expected the RCD to trip. Itwas a TN-C-S system so wondered if the shared neutral and earth may have aneffect?
The IR for L-N and L-E belled out perfectly, I haddisconnected both the neutral and earth from the board to avoid anyinterference. There was nothing plugged in or spurred, but I wouldn’t expectthat to matter anyway on N-E. The only thing I didn’t do was put a load on thecircuit – would this make any difference?
Can anyone shed any light?!?! Thanks, Andy.

hi Andy

"0 MegOhms" could mean 872,176 Ohms.

If you use Ohms Law you'll get a rough idea about the limit at which an RCD (might) trip.

it will be alot less than the above!
 
Have I got mixamatosis..... Ah apologies if I am a digit out. Not near it (on holiday) so a bit off the mark. Maybe its down to 0.1 M Ohms. Same thing though under that it'll just read "0" on alot of testers.

which isn't necessary true. So my point stands.

Sort of.

back to the San Migger
 

Reply to 0 Megohms N-E and no RCD Trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
I had a fault finding job on Thursday, intermittent RCD tripping. 2 actually, there was a 30mA RCD upstream, and a 30mA RCBO protecting the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock