Search for tools and product advice,

Discuss 100 A mains isolater to Garage unit. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
If a want to spilt the tails after a 100A isolation switch does the 2nd DB ( a new garage unit ) have to have a 100 a main switch or is a 40a RCD OK ? I’m assuming because there is a 100a isolation switch then I don’t need a main switch in the garage unit. The garage unit will only be powering a ring main 32a and lighting 6A.
 
firstly you need a switch/fuse where you split the tails. the rating of this will depend on the load and size of cable feeding the sub.
 
I see you are a trainee. Have you asked your supervising electrician about this issue ?

ive been told to spilt the tails after the main isolator. 1 feed of 25mm2 tails will feed the house and that is a 10 way board with an 100 amp main switch but then from the 2 feed off the Henley block where I will spilt it I can go to a garage board where an RCD is present as I won’t need an 100 amp main switch at that board as the 100 amp isolation switch before the henley blocks is fine. I have asked the guy I work with but as I’m OCD I check things 100 times and as lots of people.
 
ive been told to spilt the tails after the main isolator. 1 feed of 25mm2 tails will feed the house and that is a 10 way board with an 100 amp main switch but then from the 2 feed off the Henley block where I will spilt it I can go to a garage board where an RCD is present as I won’t need an 100 amp main switch at that board as the 100 amp isolation switch before the henley blocks is fine. I have asked the guy I work with but as I’m OCD I check things 100 times and as lots of people.
As Tel says, overcurrent and fault protection should be provided for the garage circuit as for all circuits. The garage board should have a method of isolation within it such as a main isolator or RCD.
 
yeah. for the anticipated load ( socket ring, and 1 lighting circuit.) the garage feed would ideally be 6.0mm, top of head , dependent on the run , installation method and VD. therefore you would need to fuse it at source at, say, 40A.this is where you'd use a switch fuse.
 
Hi - my thought is the isolation switch rating should equal or exceed the nearest upstream overload protection. If the new switch fuse after the service connector block is 40A then the existing 40A double pole RCD should be ok as a local isolator in the downstream garage board.
 
As Tel says, overcurrent and fault protection should be provided for the garage circuit as for all circuits. The garage board should have a method of isolation within it such as a main isolator or RCD.

Ok great - The garage unit has a 40A RCD this is the Method of isolation. So it’s fine then :)
 
Ok great - The garage unit has a 40A RCD this is the Method of isolation. So it’s fine then :)

You need overcurrent and fault protection at the start of the circuit which feeds the garage.
What are you installing after the 100A isolator to protect the circuit which feeds the garage?
What type of cable are you using and how long is it?
 
You need overcurrent and fault protection at the start of the circuit which feeds the garage.
What are you installing after the 100A isolator to protect the circuit which feeds the garage?
What type of cable are you using and how long is it?
I was told by an electrician that I could spilt the tails after the 100a isolation switch via a Henley block . From the Henley block I would use 25mm2 tails to a Garage Unit with a RCD of 40 a and 2 breakers or 32a and 6A.

I suggested using an armoured from the current consumer unit ( via a 40a breaker) into the back of the new Garage unit. But I was told better to spilt the tails.
 
I was told by an electrician that I could spilt the tails after the 100a isolation switch via a Henley block . From the Henley block I would use 25mm2 tails to a Garage Unit with a RCD of 40 a and 2 breakers or 32a and 6A.

I suggested using an armoured from the current consumer unit ( via a 40a breaker) into the back of the new Garage unit. But I was told better to spilt the tails.

How far is it from the origin to the garage? Is this an attached garage or detached?
 
In that case I'd just have the garage RFC on a 32a RCBO from the 'main' CU and wire the lights in the garage through a fused connection unit off the ring. The method being suggested seems needlessly complex to me with unnecessary material costs.

yes I agree but to hit some assessment criteria I have to install 2 new circuits. It also has to be at a new board. I only have one space so thought I would use the spare in the CU to have a 2nd board in the garage. But yes if I was just doing it then I would use a FCU on a ring and down fuse for the lights.
 
If the garage is very close to the main DB as you've said you could run a 6mm T&E from the spare way on a 40a breaker, either an RCBO or MCB depending on the installation method of the 6mm/ earthing arrangement etc and run this 6mm into a garage CU with seperate ring and lighting circuits. [Either with an RCD or ordinary DP main switch depending on the supply cable device] You'd then have installed 3 new circuits.
 

Reply to 100 A mains isolater to Garage unit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
893
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
303
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi can you power a second consumer unit in the garage from our main consumer unit. We have a big armed cable from the main consumer unit into the...
Replies
14
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top