Discuss 100m switch line in the UK Electrical Forum area at ElectriciansForums.net

growler

-
Arms
Reaction score
194
I have to put 25 led down lights in a garage , customer wants them all on one switch line which will be 100 metres long. I'm going to use 1mm. Should I break them down into two lots of 14 ?
 
Give more info
What kind of fittings?
Mcb rating(s)?
Volts drop if common driver unit may be an issue if 230v to lampholders still at 100m id be calculating it although you have other hurdles to get over before this


What voltage- If gu10 you must load calc them for the maximum lamp value i.e. 50watt , also a led lamp has an inrush you will be limited to the no' you can switch on at anyone time on the same mcb its to be noted that led lamp will have a DC driver inbuilt so an inductive load with a inrush on power up.
 
Last edited:
the startup current on LED lamps can be rather high !

id split the lamps on two circuits then wire them back to a single double pole contactor and then switch the contactor with the 100m switchline run.

once you've done your cable calc for the 100m run you will probably find a 1.5mm will be sufficient or a 2.5mm for luck ! lol
 
I'm with shocking on this one ! No I can't be bothered into going into the workings outs calcs wise, but 2.5, will be good through a contactor, and it will easily fit into the switch too !
 
the startup current on LED lamps can be rather high !

id split the lamps on two circuits then wire them back to a single double pole contactor and then switch the contactor with the 100m switchline run.

once you've done your cable calc for the 100m run you will probably find a 1.5mm will be sufficient or a 2.5mm for luck ! lol

The startup current on SOME LED lights can be high. Others are very well behaved. I wouldn't go to the expense of splitting the circuit or adding a contactor without finding out the characteristics of the proposed lights.
 
Really ?????
Use triple pole switch or double pole , split ccts into rows , 10A type c mcb, jobs a gooden!

No need for 2.5s or contactors.
 
Last edited by a moderator:
Why is this switch line 100m long anyway?

Depending on the overall configuration of the circuit, you might be running into problems with volt drop (as mentioned before) or Zs, depending on the length of the supply cable and the rating and power factor of the lights.
 
Without more input from the OP this thread can't go any further we just don't have the info and all the speculation may be just a waste of time ive reserved my comments until we know more .... until then we might as well play it safe and use 6mm over 3 circuits and save any calcs etc ;)
 

Reply to 100m switch line in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
742
I have a staircase about 25 feet long with two recessed lights (one up top, the other at the bottom). Each light is on its own 3-way switch, which...
Replies
2
Views
774
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi, I am restoring an old art deco, wall mount medicine cabinet. The cabinet has an 18” fluorescent light tube on each side. Before I put a lot...
Replies
0
Views
385

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock