my house has 100ms time delay rcd main switch. why would this have been installed in a house? is it legal?
thanks
thanks
Discuss 100ms time delay rcd on main domestic unit?g in the UK Electrical Forum area at ElectriciansForums.net
there is a 30mA Rcd half way down the bus
would this setup be acceptable for eicar or unsatisfactory?
also, there are two breakers which are lableled cooker and central heating, these are unused the wires go nowhere, , its lagacy of old house, cooker and ch are on kitchen ring now
should it fail eicar for this?
ta
dont worry im not diy,
Unable to locate cooker circuit but it's on an incorrectly rated MCB?high impedance on 25 on circuits 2 and 3
unable to locate cooker circuit
unable to locate water bond -no continuity to earth
100 ma TD main switch
unable to locate heating circuit
wrong size mcb on cooker circuit 40A
wrong size mcb on shower circuit with 6mm cable 50A
all these have code c2
im a bit annoyed since..
we no longer have an electric shower it runs off the combi boiler,
we have a gas hob, and the fan oven is rated low enoug for the kitchen ring,
the cooker circuit serves nothing
you say the `wires go noware`...if so...have these cables been taken out of the terminations at the board?there is a 30mA Rcd half way down the bus
would this setup be acceptable for eicar or unsatisfactory?
also, there are two breakers which are lableled cooker and central heating, these are unused the wires go nowhere, , its lagacy of old house, cooker and ch are on kitchen ring now
should it fail eicar for this?
ta
Unable to locate cooker circuit but it's on an incorrectly rated MCB?
I'm at a loss to understand why he would code an S type RCD as a C2
What does "high impedance on 25" mean?
high impedance on 25 on circuits 2 and 3
unable to locate cooker circuit
unable to locate water bond -no continuity to earth
100 ma TD main switch
unable to locate heating circuit
wrong size mcb on cooker circuit 40A
wrong size mcb on shower circuit with 6mm cable 50A
all these have code c2
im a bit annoyed since..
we no longer have an electric shower it runs off the combi boiler,
we have a gas hob, and the fan oven is rated low enoug for the kitchen ring,
the cooker circuit serves nothing
Aye, could be mateMaybe high impedance on ZS.
i hired this company off mybuilder.com, for a landlord cert, eicr. they were cheapest quote,
Oh dear! Not everyone on there is bad though. The earth bonds are supposed to be visible and accessible.i hired this company off mybuilder.com
sorry what is Zs? you could be right ive read it wrong as 25
i hired this company off mybuilder.com, for a landlord cert, eicr. they were cheapest quote, but im getting the distinct feeling they are trying to pad it out.
i actually said to the bloke when he was here sucking his teeth, why cant the mcb for non existant cooker and shower just be disconected and if any wires going to them, cut them well back. apparrently he was happier just to fail it...
im still unclear on the watermain earth though, do you have to absolutely see the connection on the water main within ?? mm of the stopcock to "pass "?
i have to say thoughi realy apprciate all the advice and no, im not going to peru
landlord cert, eicr.
im still unclear on the watermain earth though, do you have to absolutely see the connection on the water main within ?? mm of the stopcock to "pass "?
Says it all really. Buy cheap, buy twice.they were cheapest quote,
seems strange there is no hard and fast rule on the water earth, one persons c2 is anothers c3.. can this be right?
ok, i know this is not true test but just to stir it up, ive just stuck my multimeter neg in the earth prong of a scoket and other side to kitchen tap,: 4.5 ohms, sounds pretty connected to me and imagine you too. thats what i mean, they are taking the proverbial, ok, maybe they couldnt find the bond, but thats no reason to say its not earthed when it obviously is, right?
Please stop poking things in sockets mate.ok, i know this is not true test but just to stir it up, ive just stuck my multimeter neg in the earth prong of a scoket
sorry what is Zs? you could be right ive read it wrong as 25 "?)
ok, i know this is not true test but just to stir it up, ive just stuck my multimeter neg in the earth prong of a scoket and other side to kitchen tap,: 4.5 ohms, sounds pretty connected to me and imagine you too. thats what i mean, they are taking the proverbial, ok, maybe they couldnt find the bond, but that is no reason to say its not earthed when it obviously is, right?