I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with 1.5 flex from the oven. (manufacturer) I'm trying to argue that this needs a fused spur before connecting to double oven connection unit as 40 amp MCB is too high to protect 1.5 flex under fault conditions. Instructions say connect straight to double oven connection unit. Any expert opinions please. I'm sure I've explained it correctly
 
4mm cable is undersized for a 40A supply, the minimum that should be is 6mm but may need to be bigger due to de-rating factors.

As an oven is an appliance not subject to overload the 1.5mm flex may well comply as long as it is suitably protected against fault by the MCB.
 
Basically though The 40 amp MCB would not protect a 1.5 mm flex and would require a fused spur to protect against short circuit. As you said overload should be ok. It's the 1.5 flex cable that comes with oven I'm concerned about
 
Basically though The 40 amp MCB would not protect a 1.5 mm flex and would require a fused spur to protect against short circuit. As you said overload should be ok. It's the 1.5 flex cable that comes with oven I'm concerned about

No, the 40A MCB may protect the 1.5 flex against short circuit, you would need to do the maths to confirm that.

I didn't say overload should be OK, I said an oven is an appliance not subject to overload faults.

A fused spur would not be suitable if the oven requires a 16A supply as a fused spur is limited to 13A
 

Reply to 16 Amp Oven installation with 1.5 flex supplied in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
841
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock