Discuss 16mm T&E in the UK Electrical Forum area at ElectriciansForums.net

7029 dave

-
Mentor
Esteemed
Arms
Reaction score
3,927
I had a job last week to provide 6 meter connections . New builds and noticed in the meter box, Electricians had run in 16mm t&e from CU to external box with 80amp switch fuse.
Thoughts please.
 
OK for CCC on line and neutral, if a TNCS supply then the earthing conductor is undersized, if TNS then probably OK.
If buried in the wall <50mm then needs 30mA RCD protection, though most DNOs do not bother protecting tails from cut out to meter when buried in the wall!
How are the live conductors terminated in the switch fuse as it is normally hard to get a fully enclosed live conductors from a twin and earth cable without leaving exposed insulation.
 
OK for CCC on line and neutral, if a TNCS supply then the earthing conductor is undersized, if TNS then probably OK.
If buried in the wall <50mm then needs 30mA RCD protection, though most DNOs do not bother protecting tails from cut out to meter when buried in the wall!
How are the live conductors terminated in the switch fuse as it is normally hard to get a fully enclosed live conductors from a twin and earth cable without leaving exposed insulation.

The earthing is TNCS , did notice a 10mm earth conductor with the t&e, still on first fix so nothing connected , I can only assume they have run it together. Forgot to say, on one of the other plots not boarded up yet, the run from the meter box to CU position was less than 3 meters. IMO 25mm tails should have been run.
 
If clipped direct it justs complys I prefer to fuse at 60A as Richard has just posted if within wall 50mm rcd protection but this brings another problem of a fault the whole house tripping out in the m/box a small switch fuse is usualy used ,if down the cavity you have issues with derating for insulation,(also watch out for polestyrine ball insulation)protection of cable sharp edges.In my previouse job before metal c.u came in to the regs we ran 3 core 16mm swa in earthing swa one end in metal box into small switch fuse. If the builder would not install other meter box.we also ran the swa internally in line with socket so in a zone.
 
If any extraneous conductive parts exist then these could be bonded back to MET with 10mm being tncs Rather than the CU. how do you know the installer wasnt going to use a 63A fuse in there if it was at 1st fix stage? If the 16mm is conected to a sw fuse why would you not then treat it as a circuit and then do an adiabatic to work out the cpc.
He who sticks his nose in a wasps nest will get more than a nostrill full of honey comes to mind here!!
 
If any extraneous conductive parts exist then these could be bonded back to MET with 10mm being tncs Rather than the CU. how do you know the installer wasnt going to use a 63A fuse in there if it was at 1st fix stage? If the 16mm is conected to a sw fuse why would you not then treat it as a circuit and then do an adiabatic to work out the cpc.
He who sticks his nose in a wasps nest will get more than a nostrill full of honey comes to mind here!!

Don't really get you, I was not being nosy, just interested .I could not careless if at the meter box, it was presented with bell wire. Use self connect meters it's the Sparky that will be connecting up his installation. The switch fuse was screwed to the back board all on it's own and it was 80amp.
 
OK for CCC on line and neutral, if a TNCS supply then the earthing conductor is undersized, if TNS then probably OK.
If buried in the wall <50mm then needs 30mA RCD protection, though most DNOs do not bother protecting tails from cut out to meter when buried in the wall!
How are the live conductors terminated in the switch fuse as it is normally hard to get a fully enclosed live conductors from a twin and earth cable without leaving exposed insulation.


You'd use the small tapered cover that fits on the outgoing side of the switch fuse Richard. [Sometimes known as a transition cover ?].
 
Generally with 16mm t&e a separate 10mm is run for bonding and the CPC of the 16mm T&E is just that..... A circuit protective conductor.

I used a bit of 16mm T&E as a distribution circuit on a new build the other day due to aesthetics. I've had a separate meter box installed to house the switch fuse next to the actual meter box. I've run the cable up the wall internally through joists and down to the consumer unit. I've used a metal capping that the manufacturer states provides adequate protection from nails, screws and the likes of.

Reason I chose to use 16mm T&E over 16mm SWA is the consumer unit is installed on show in a utility room and an SWA glanded in top or bottom would look rubbish IMO.
 
cant see a issue with it, we used to do this all the time. After a communal job we would have some left and would wire 2 bed's with it (supply). As long as there is a 10mm with it as well and there is some form of mechanical protection in place it seems sensible. Keep your nose out ;)
 

Reply to 16mm T&E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
372
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
250

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock