Out of interest what's most commonly used?
Discuss 1mm or 1.5mm T&E for standard lighting circuit in your average house. in the Lighting Forum area at ElectriciansForums.net
Even if you halved 1mm's ccc (method C), it would still be 8A.1mm unless there is loads of Insulation surrounding my cables e.g. Celotex, Kingspan
1.5mm2 don't know what Shirley usedShirley (!) you use a cable suitable for the design, not 'cos of its physical size?
If it satisfies the design then using size as a consideration is legit Shirley ?Shirley (!) you use a cable suitable for the design, not 'cos of its physical size?
If it satisfies the design then using size as a consideration is legit Shirley ?
I use 1.0mm almost exclusively, and the reduced size helps considerably on most rewires. Never have a problem with design considerations.
Possibly ?Me thinks you misunderstood my post?
Even if you halved 1mm's ccc (method C), it would still be 8A.
Sure about that ?
I think 6A is the most onerous ref method in the OSG for 1.0mm
I'm misunderstanding yours now
You couldn't totally assume 1.0 is ok in all circumstances you could invent. Never mind volt drop for now, but if there are 20 circuits bunched in 50c ambient under insulation you'd have to do a bit of redesign.
Agree hence the caveat about"circumstances you could invent" as it's not realistic to encounter that!We are talking about an average house.
Maureen, I need a hand down here....pint or a half
No but go on......
Agree, sorry wasn't disagreeing with anyone, just trying to add somethingI don't think anyone is assuming that.
Agree, sorry wasn't disagreeing with anyone, just trying to add something
Another point is if you might want to repurpose some of the cables in future as "power" instead of "lighting"you'd be better with 1.5
I've often thought I'd be better off without lights and having sockets on the ceiling instead
Perhaps John is older than me (but younger than Tel), when we did just that, plugging the iron into the lighting point.
You couldn't totally assume 1.0 is ok in all circumstances you could invent. Never mind volt drop for now, but if there are 20 circuits bunched in 50c ambient under insulation you'd have to do a bit of redesign.
I used to mainly use 1.5mm, but due to LED lighting now mainly use 1mm
10-15 years ago everyone suddenly started wanting loads of GU10 down lights in each room. Even though 4 would be ample, customers wanted 6,9,12 down lights in each room. This was when you would use a 50W or 35W GU10. Added to that the wall lights the loading soon added up. As I said in my post when people started using LED the loading dropped dramatically.This kind of statement never makes sense to me, the average domestic lighting circuit is put on a 6A mcb with cable size calculated accordingly.
Lee,Out of interest what's most commonly used?
That def sounds like your average house doesn't it! Sorry I took so long to reply but my computer was in the pool house, 50 meters down the corridorLee,
Surely ... or is that 'Shirley' ... there is no 'standard' house and therefore the BS 7671 design rules need to be applied effectively! I am working in a large (?) Georgian property at the moment and the landing lighting circuit is > 50 m in length. Whilst nominal 230 V LED lamps may be fitted, and who would want to replace 8 lamps in each of 2 chandeliers with 100 W incandescents, it is theoretically possible even if the light fittings are not designed for 0.8 kW for someone to do so!
Lee,That def sounds like your average house doesn't it! Sorry I took so long to reply but my computer was in the pool house, 50 meters down the corridor
So you would walk in to your typical, average 3 bed semi to quote for a rewire....you would then apply the design rules as you put it of BS7671 or you would know without a shadow of doubt that a 1mm lighting circuit will be absolutely more than adequate because you are an experienced electrician without putting pen to paper?Lee,
I didn't for one moment imply that the house that I am working on is 'standard' or 'average' ... merely that effective application of BS 7671 design rules are required in every case!
This thread is about "standard lighting circuits in an average house", not about large Georgian properties. We're not talking 8 lamp chandeliers, more single white plastic pendants in the middle of each room, possibly 2 in the lounge.Lee,
I didn't for one moment imply that the house that I am working on is 'standard' or 'average' ... merely that effective application of BS 7671 design rules are required in every case!
... clearly ... as you put it like that ... 1.0 mm2 every time!So you would walk in to your typical, average 3 bed semi to quote for a rewire....you would then apply the design rules as you put it of BS7671 or you would know without a shadow of doubt that a 1mm lighting circuit will be absolutely more than adequate because you are an experienced electrician without putting pen to paper?
Personally I always use 1.5 I hate 1.0mm2 for a few reasons if the attic gets more insulation after I’m away then guaranteed the insulation will be laid over the cable reducing the ccc and if the customer decides in a few years to put up a chandelier in the hall the living room and a bedroom with 6 halogens in it and halogen downlights in the kitchen etc then there is the potential for overloading I also hate terminating 1.0mm it’s easy enough in wagos or ceiling roses but I always end up chopping it in the earth and nuetral bars of a CU even when it’s doubled over because it’s so thin and crappy just my personal preference
I believe there's still an argument for installing sealed unit LEDs, especially if you're planning to use 1mm.
I thought I'd explained that in the previous paragraph - it's so the end user can't change a 7w light bulb for a 100w light bulb, thereby potentially messing up calculations or burning something next to it or whatever. In certain situations the tenants take the light bulbs out and steal them, so there's an argument there as well.What argument is that then? In what application would you select a cable size and then select your light fittings based on the size of the cable?
You never heard of diversity?I thought I'd explained that in the previous paragraph - it's so the end user can't change a 7w light bulb for a 100w light bulb, thereby potentially messing up calculations or burning something next to it or whatever. In certain situations the tenants take the light bulbs out and steal them, so there's an argument there as well.
yeahYou never heard of diversity?
I do agree to an extent but I still just prefer to install 1.5mm2 just makes me feel better? Think its all down to my journeyman instilling in me that 1.0mm was the devils cable and starting out my career in mostly commercial buildings that usually the minimum csa was 2.5 for lights and boy were they a bugger to install in a tamlite emergency bulkhead with the wee PCB terminals. I know there aint really no rhyme or reason I just wouldn't consider 1.0mm and always default to 1.5 unless the calcs specify bigger....But there's no rhyme or reason for your concerns.
1mm smothered with insulation, #6 with 6A ocpd, will be fine. With a 1.5mm, that could be 10A, what ocpd could you use, that would improve on 1mm?
An RFC could easily be overload, once you step out of the house. Wire RFC in 4mm?
1mm & 1.5mm have the same size cpc.
So that just leaves your nuetral?